I have an older PLC, a 1756-L55 (Logix5555) with 13.03 firmware.
And, I have a newer machine being installed that needs to talk to this older PLC.
The new PLC is a 5069-L310ERMS2. Probably programmed with Studio 5000 V31 or greater.
What is the best way to see I/O tags in each PLC from the other PLC?
A colleague mentioned something about Produced and Consumed tags.
Is that the right approach?
Is the MSG command an choice?
Using Produce/Consume in your application is going to be problematic. With older firmware version the Consuming PLC needs to have the Producing PLC in its I/O tree. The problem is the version of RSLogix that you will have to use to configure the PLC won't recognize a 5069 type CompactLogix. Message instructions should work but keep in mind the 5069 uses a different path structure than a 1769 does.
Long and short is you should be able to accomplish what you are trying to do but it's going to be complicated.
Having said that, and I'm hesitant to say this because I don't want to make this a "sales" post, but Spectrum Controls Universal Gateway will do it pretty easily without any PLC programming. It will read the tags from one device and write them to the other and vice versa. The only thing you will need to add to each PLC is the corresponding tags I.E. for each tag you read from one PLC you will need a tag in the other PLC for it to be written to.
Produced/Consumed tags have been around since RSLogix 5000 v1. You can easily make it work in this application, and for my money, I'll choose produced/consumed over explicit messaging (MSG instruction) any day of the week. With a MSG instruction, there are a lot more things that you have to get right, a lot more manual configuration to be done, and if you miss one thing it might kind of work or not work at all. My experience with produced/consumed is that there are just a couple of things to remember, and then it just works.
First up: create a UDT with enough space for all the data you can ever envision sending. Then double it in size. e.g. if you have 20 BOOL tags, 5 DINT tags, 10 REAL tags and 2 STRING tags, make a UDT with two DINT's for BOOL data (which gives you 64 BOOLS), followed by say 20 DINT's, followed by say 30 REAL's, followed by say 10 STRING's. A produced/consumed UDT can't be changed online, which is probably the main drawback they have when compared to MSG. But if you put a bit of thought into it before you set it up and give yourself plenty of spare space in your structure, you can mitigate it for 99% of scenarios.
Once your UDT is created, export it and import it into your other PLC. You could manually create it in the other PLC, but export/import ensures that it will be identical and there won't be any data entry errors.
Next, put the CLX into the 5069 Compact Logix's ethernet I/O tree, and vice versa. With the 5069 compact logix, this is easy - it knows about all of the old PLC's. You'll need to start by adding the ethernet module of the CLX rack, then the processor.
Adding the 5069 into the CLX ethernet tree is obviously not directly possible, because the older CLX doesn't know about the existence of the newer 5069 Compact Logix. However, if you get it "close enough", it'll work. Add in a 1769-L35E with the 5069's IP address. The 5069 will receive a message addressed to it, but structured for a 1769-L35E, and knows what to do with it. It will respond with the correct data accordingly.
Finally, create two instances of your UDT in both PLC's. Call them something like "CommsIn_FromPLC1" and "CommsOut_ToPLC1". The "CommsOut" tag will be a produced tag. The "CommsIn" tag will be a consumed tag, and you need to point it at the producing PLC, and tell it what the produced tag at the other end is called.
If it were my application, I'd have a play with this before getting too deep into MSG instructions. If you have to learn either option from scratch, P/C tags has a much shorter learning curve.
One final tip: because you're using one of the new-style 5380-series Compact Logix PLC's, there are some important caveats with using UDT's for communication with regard to how you structure those UDT's. This applies whether you're using produced/consumed or explicit messaging. Have a read through pages 96 to 102 of this document for details. It is a bit wordy, but hopefully you can make sense of it enough to make sure you avoid the issue it describes. If not, post back what you're unsure of and we'll try to help further.
Good luck!
I have two cells. They are identical (almost). Each cell has a Contrologix 1756-L73 processor and a 1756-ENBT addressed at 192.168.1.10. Each...
29
6,266
Hi all, I've only worked on Profinet once before to talk between a few S7-300 PLCs. I managed to get the system communicating by using the "GET"...
2,627
When a new machine comes into our facility the PLCs and Variable Frequency drives typically come with their IP addresses in the 192.168.1.XX or...
6,159
Hello everyone. I am a soon to be downsized(rightsized?)employee of a large multinational tool company. I am trained as a machinist, but for the...
2,646
  • Locked
Hello everyone. I am thinking about buying a book on plcs. I am wondering what is the absolute best one on the subject. Does it matter if a book...
6,191