Bit at ControlLogix reset after SCADA shutdown
flyers
Sep 2006
Amk
295
Hi guys,
My colleague is facing a problem at site where the SCACA (FT Talk SE) and PLC (ControlLogix). There is a push button to bypass the alarms function in the PLC, when click once, bypass is enable (bit set to "1" in PLC), when click the 2nd time, the bypass is normalized (bit set to "0" in PLC).
This is working well, until he shutdown/restart the SCADA workstation (FT Talk SE), once the workstation is shutdown, the enable bypass bit automatically reset to "0". All the alarm bypass normalized automatically. Meaning we can't shutdown the SCADA workstation when we want to bypass the alarms.
Does anyone knows if there is any setting that we missed out or should check with?
Thanks.
What type of button did he use? Maintained maybe..
You could switch to momentary and do all the coding in the PLC if it isn't already this way.
HTH
HTH
He's using maintained type. There is no other way we can do it without disturbing the PLC (system is running). Is this condition normal for FT (when SCADA shutdown, bypass bit normalize to '0')?
You need to describe better what you are doing.
What is an "Alarm Bypass Bit" ? There is no such FTView built in device, so it is something that you guys created.
Also, FTView does NOT write values out to tags on shutdown (it hardly writes them out when commanded to), unless you have scripted it to do so.
And why can you not 'Disturb' the PLC, ControlLogix fully supports online editing.
folks, I have a controllogix 1756, DO Card (OW16) connect to 1492-IFM40F-F120-2. I did a test at a pin on 1492-IFM40F-F120-2, Force a bit on, and...
2,829
Hi, I have a 1756-a17 rack with a 1756-L61 processer. There is three 1756-OB32 cards installed amongst various other cards. About twice a month...
3,336
I have a PLC5 program that I converted to Logix5000 platform with the automated translation tool. Everything went fine with that, but my problem...
3,252
Hi guys, I've got a basic question about how the "S:FS" bit is handled in CLX processors. I'm wanting to trigger some anti-diameter reset logic on...
10,738
Is it possible to Map a Logix Dword or a Word bit as a Tag in Redlion G3? Basically I want to have a DINT Tag from Logix as a Single (not an...
1,835