Broken wire, twinCAT
damjaniii
Feb 2014
Maribor
Hey guys. I'm developing a system that will sound an alarm if the wire of the encoder is broken. I am talking about sin/cos encoder, and i haven't done it yet but i made a test sin and 90 degrees shifted cos signal so i can test my idea. I want to ask about the condition in which i should sound the alarm of broken wire. Here's my code, and my condition is SINUS = COSINUS. Is that right or i should make sinus+cosinus=sinus or sinus+cosinus=cosinus or sinus+cosinus=0 THEN break wire, and why? Thank you :)
Im actually trying to find the situation when the wire is broken. if one wire is broken, sin or cos, depend which line do we break is turned to 0 while the cable is broken .... so at some point sin will be equal to cos, that is the point when i realise that the wire is broken or cut... Why is this wrong and how would i use pytaghoras? Thanks and sorry for bothering you.
Sorry for a late reply. Check first that your encoder doesn't have this functionality already. I am working with one that has a "fault" wire output for when it senses such a discrepancy between the A & B quadrature signals.
for one you dont know at wirebreak if input goes to 0 as the input has high impedance.
You will have to make your calcs with sin*sin+cos*cos > 0.9, whenever lower the circuit has a problem.
Good afternoon forum members. We recently had a fuse blow on the wiring between a 1756-OF6CI analog out card and a control valve (which we have...
2,663
See the Codesys LD program below; I would expect Rungs 2 and 3 to produce functionally identical results, but they do not. Does anyone have any...
36
2,027
Hi All, Have got a problem which i first thought to be a network problem but now starting to think we have got a broken 1734-AENT PointIO unit...
29
4,491
Hello Guys. One question. I have to restore a project from a broken OP177B mono(Version 1.0.1.0), to a different OP177B mono panel (Version...
2,838
Have failed Red Lion DPSX000 data station is it possible to upload the configuration file to download file to new unit
1,006