1. i am getting voltage feedback from welding power source of (0-10VDC) which includes peak and base voltage for time duration of 0.2 sec
i.e i am getting voltage feedback of (5vdc 0.2sec time delay 4vdc & 5.2 vdc 0.2 sec time delay 4.2vdc.etc etc etc continuously ) so 5vdc first value is peak voltage and 4vdc is base voltage) ,
this feedback voltage i am connecting to plc and in plc program i want to display only peak voltage by neglecting base voltages (i. e in HMI scree i must only display peak voltage ) is it possible to record data with respect to 0.2sec speed .?? can anyone help in programming (micrologics 1500 AB plc)
Your question isn't particularly clear but to record a peak value of anything is pretty straight forward. Compare the value you are monitoring (Value A) with another register of the same data type (Value B) and whenever Value A is greater than Value B move Value A into Value B. Or have I misunderstood your question?
Hai Beethoven , thanks for your reply .
but
1.how to separate peak and base voltages with one continuous analog signal (0-10VDC) with fast change of 0.2sec/0.15 sec
Your peak voltage is always higher than your base voltage and you say you only want to display the peak value so why do you need to separate the 2?
consider this is analog signal , with in this signal we have peak and base voltages and these voltages are keep on varying based upon ARC voltage/length (5- 0.2sec - 4 & 5.2-0.2sec -4.1 & 6-0.2 sec -5 & 7-0.2sec -6.1 etc etc continuously ) like pulses...
Note:As u said if i separate Value A and Value B ..my job is done no need of comparing values ..i can directly display values A ,,But i need to monitor peak(value A).
Have you tried to capture the data yourself or monitored it in the PLC program. I am not a AB man myself but there is a wealth of knowledge on here that will help you but they will want you to show what you have done yourself then they will guide you through it.
I think I'd record samples at a .1 second rate and remember three or four
samples. The sample with the highest value is the peak.
See attached example. This example stores a sample every 0.1 seconds in a four integer stack. The voltage is scaled to millivolts. First thing it does is copy the stack down one, so N10:1 is copied down to N10:0, then N10:2 copies down to N10:1, N10:3 copies down to N10:2. Then the newest reading is stored at N10:3. That way your PLC remembers the last four readings. (The COPy has to move data down, it can't move it up or it will just fill the whole stack with N10:0.) Then the program searches N10:0 through N10:3 for the largest value. After if finds the largest value it divides it by 10 and stores it at F8:0
I have one more idea .. ( this is related to TIG Welding machine -Fronius )
this analog signal is for voltage feedback and i will take current feedback by connecting CT from one terminal of the cable (+/-) the feedback from CT is o-10vdc with respect to 0-1000vdc pulse signals , this is the exact peak & base current with out any disturbances ...
by using this analog i can do any thing better ...to read only peak voltages ...... THIS IS FOR AUTOMATIC VOLTAGE CONTROL ...
So you say it is jumping between peak and base every 0.2 seconds?
so the wave is square.
just take samples anytime.
If sample is below average it is base if above it is peak.
have a moving average of 10 samples,
another way is to look at it like asynchronous communication, if you see a flank wait 0.1 second and take a sample, wait till next flank and wait again. (this will need a fast PLC.
Hello everybody, I believe that I will find experts here who have already solved a similar topic. I need to calculate the length of the...
349
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
119
Hi!! I'm looking for Temperature rise calculation software from Rockwell, I just download "Product selection toolbox 2022" but this software is...
226
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
120
I might be overthinking my problem, but I need some help. I am trying to write a formula in my plc to calculate the footage of paper being...
630