Capacitor
Nick.Ferguson
Sep 2011
Nebraska
24
This is not a plc question but hoping you guys can help. My boss would like to lower the in-rush current on an 120 VAC motor. The motor never had a capacitor on it before, can one be installed in series? Some of the stuff I have read says to size 50% larger on voltage and a formula of 2655xI/V to find the μF.
Well my question is can a capacitor be installed on a 120 VAC motor with one set of windings,and will it reduce in-rush current
Yes, but only because the capacitor has internal resistance. ESR. This is not the correct way to do it. Capacitor will have a short life.
A VFD is about $100.00 for a small motor. This is the best way.
YES you can if you want.
PROBABLY NOT - you are just adding a load and one that has its own in rush current in addition
Reading between the lines -
increase your wire size you are having line volt drop problems.
Further help requires information you did not supply. Please supply copy photo of motor nameplate and describe the driven load OR
supply crystal ball
Dan Bentler
Simple answer, yes. Complex answer, it depends. What happens is the voltage and current will be reduced at the motor winding(s), depending on the capacitive reactance value introduced. It also reduces everything else, HP, torque, etc.
Well my question is can a capacitor be installed on a 120 VAC motor with one set of windings,...
Yes to this part of your question. You can install about any device you want to, but whether it will help you depends on what you are trying to do.
To reduce the in-rush current, you have to spread the motor "starting current" (the power it takes to overcome the inertia of the motor AND driven load) over a longer time period. An AC capacitor will not do that because it charges and discharges 60 times per second.
Starting the motor at 0 speed and slowly increasing to 100 % full speed is probably the best way to reduce motor starting current. A small soft-start electronic motor starter will do that, but you may have to change out your motor for a different type.
Hey guys, I know this is not PLC related but many of you are pretty crafty. I need to resurrect an old PowerFlex 700 VFD. AB calls for reform...
2,330
I came across some information concerning reforming of capacitors in VFD's that have been stored for more than 2 years. We have quite of few that...
2,387
Hello Everyone, In need of some most needed help on troubleshooting a Kinetix 6000 servo. The first one smoked and was replaced only to smoke...
1,281
Hi all, there is something that is not making sense to me. Upon system powerup, twice in a row two brand new Sinamics PM240-2 started smoking and...
1,600
Somewhat off topic but wondered if anyone could give me a place to start. Last year a customer wanted a very rough and ready and cheap speed...
2,511