Channel configuration for ML1400 PLC
shailesh_vb
Jun 2013
Pune
43
Hello everyone,
I have doubt regarding ports of Micrologix 1400 PLC.
Channel 0 and Channel 2...
Channel 0 is Rs232C or RS485 or can be configured as both?
Same for Channel 2..
Because I did Modbus RTU Slave on Channel 0 and checked it with Modscan software. And used no RS485 to RS232 converter in between PLC and PC.
Thanks,
Shailesh.
Not quite sure what your question is, but CH0 (8-pin mini) can be used with either RS232 or RS485. CH2 (9 pin D-Type) can only be used with RS232
Hope this helps!
Regards,
Rob
Thanks for Reply.. My question was can we use Channel 0 for both RS232 and RS485 communication? I am doing Modbus RTU slave.. I wanted to read more than 2 slave devices
at a time on Master PLC.
And Yes I got it. For Channel 0 when I use 4 and 7 pin of connecter, then I think channel 0 can be used for RS 232 communication. And when I use pins 1 and 8 of connector, then i think channel 0 can be used for RS485(multidrop) communication.
I tried it yesterday.. and I got result..
Thanks,
Shailesh
I started this reply yesterday but got called away before I finished it. I'll post it now anyway for further clarity with regard to the ports in question.
MicroLogix 1400 User Manual said:
The MicroLogix 1400 controllers provide three communications ports, an isolated combination RS-232/485 communication port (Channel 0), an Ethernet port (Channel 1) and a non-isolated RS-232 communication port (Channel 2). The Channel 0 and Channel 2 ports on the MicroLogix 1400 can be connected to the following:
• operator interfaces, personal computers, etc. using DF1 Full Duplex point-to-point
• a DH-485 network
• a DF1 Radio Modem network
• a DF1 half-duplex network as an RTU Master or RTU Slave
• a Modbus network as an RTU Master or RTU Slave
• an ASCII network
• a DeviceNet network as a slave or peer using a DeviceNet Interface
(catalog number 1761-NET-DNI)
• an Ethernet network using the Ethernet Interface module
(catalog number 1761-NET-ENI, or 1761-NET-ENIW)
• a DNP3 network as a Slave
When connecting to RS-485 network using DH-485, DF1 Half-Duplex Master/Slave, Modbus RTU Master/Slave or DNP3 Slave protocols, the MicroLogix 1400 can be connected directly via Channel 0 without an Advanced Interface Converter, catalog number 1761-NET-AIC. The Channel 0 combo port provides both RS-232 and RS-485 isolated connections. The appropriate electrical interface is selected through your choice of communication cable. The existing MicroLogix 1761 communication cables provide an interface to the RS-232 drivers. The 1763-NC01 cable provides an interface to the RS-485 drivers.
So...
shailesh_vb said:
Hello everyone,
Correct. By selecting your protocol and using the correct cable the Channel 0 port will be auto configured as either an RS-232 or RS-485 electrical interface. You can connect directly, using only a cable, as this port is electrically isolated from the device or network you are connecting to.
Same for Channel 2.
Not correct. Channel 2 uses an RS-232 only port. You can select the same communication protocols as Channel 0, except that where a protocol uses an RS-485 electrical interface, such as MODBUS, you must use an RS-232 to RS-485 converter, such as a 1761-NET-AIC. Also, because Channel 2 uses a non-isolated port, when using RS-232 communication protocols, it is best practice to use the 1761-NET-AIC as an optical isolator between RS-232 devices.
You know it works, but now you know a little bit more about why it works.
Thanks,
Shailesh.
G.
Hi Experts, I am new to this forum and have a question regarding AB MircoLogix 1100 Ethernet port IP configuration. As per the ML1100 User...
2,900
Hi, I am working on RSlogix5000 and using a PID controller to control a Fail Open valve. Now when the controller output 100% (20mA), the valve...
2,511
Hello guys, I will continue with beginners questions, when I was explore our factory system in slc 500 software (SLC 5/04) into folder ‘channel...
5,167
i am using analog NI8 slc 5/03 but i dont know what is purpose of 8 different channels available and which i should be using to start with also i...
1,504
I have read the manual, but still confused, must be one of those days, hoping someone on here can help me see the light. Have a slc505 that has...
2,887