Cheap solution to read temp. on analog in?
Icefire
Feb 2007
MTL
37
Any way to read a thermistor/thermocouple on a GE 90 Micro Analog Input?
0-10V, 0-20mA or 4-20mA?
I tryed with a LM35DZ chip which give 10mV/*C, too sensible/not enought resolution.. since the PLC resolution is 10mV.
I want to read around 60-90F
How much more resolution do you need? If you use an LM34 in place of the LM35 you will get 1.8 times better resolution. An LM34 will give you 10mV per degree Farenheit instead of the 10mV per degree Celsius that you get with the LM35. So 60-90F gives you 600-900mV instead of 150-320mV.
I was using a LM324 With a non-inverting gain of 10, I got 2.546 volts but the PLC's value fluctuate +-0.2V.
Maybe something with the analog input..
It's a GE 90 Micro
It's a GE 90 Micro
Add a low pass filter; either RC or use a spare op-amp in the LM324?
Or even filter it in in the PLC?
It's a GE 90 Micro
What's the distance from sensor to PLC? And were did you place the LM324?
Kind regards,
the circuit was on 2 feet from the plc on a pratice breadboard.
I think it has something to do with the inner values of the PLC.
The A/D can be calibrated.
Hey everyone! Let me start by explaining what I want to do here, I’ve got a small PLC system and am looking for a cheap way to rig up a compact...
4,394
Hi y'all, I am looking for affordable and reliable PLC and HMI solution : PLC with real-time clock and multiple (>16) relay output, modbus...
17
10,372
Hello to all, I have a need to make small process HMI solution to incorporate 3 analog and 5 binary signals. Problem is that HMI display must be...
2,971
Anyone know of a cheap foundation fieldbus communicator? Something like the USB 8486 H1, but one that does not cost $3k? Thanks, Trevor EDIT: I...
128
89