Citect comms to Hirschmann Switches
josh_d
Jan 2011
Vic
20
Hey guys,
Has anyone had any luck / know if it's possible to use Citect to monitor status data and statistics from a hirschmann managed switch?
I got in touch with Citect support and they said to check out the SNMPII driver.
Thanks,
Josh
The Hirschmann switches I have used all supported EtherNet/IP as well, so in theory you could use an EtherNet/IP driver to read the parameters that are exposed. In practice, though, it's not so simple. EtherNet/IP has various forms of communications and can be extended so simple 'we support EtherNet/IP' really does not mean it is compatible with any other particular device.
The Hirschmann device will do Class 1, UCMM, and Class 3 comms with various objects yielding lots of different information, all in the user manual. However, looking at the Citect drivers in the past, they are specific to Rockwell and the vendor extensions they have created for getting tags out of Logix5K devices (have done this), and I suspect there is a driver for PCCC over EIP to get data out of Logix500 devices. In either of these cases, the service codes and object/instances are fixed to the Rockwell extensions so are not useful for general EIP communication using UCMM or Class 3 explicit messaging. Citect definitely does not support Class 1 or IO communications natively, though with a a Hilscher or Molex adapter in the PC it may be possible to go this route, but not sure it's worth the trouble.
So after all that, I would either:
1. Use SNMP driver in Citect
2. Use EtherNet/IP and feed the data into a controller, either Rockwell or Schneider, and then expose the data that I wanted from there, which Citect then has a fieldbus driver for either platform.
Hi, I'm a first time poster. I need to establish a connection between an FX5U PLC to a Citect PC. I will be using a MODBUS TCP - MODBUS SERIAL...
3,991
Hello All, I am running Citect SCADA 2018 R2 and trying to connect to a AB ControlLogix L81E. I have configured the board, port and IO device...
1,935
Hi guys, I have a client with a siemens S7200 PLC (1215C CPU),which has an on board ethernet port (marked "profinet" on the PLC) and I need to...
1,539
Hi, Is there an easy way to zero all the data from a device when the comms fail? We pull data from some BACNet devices into the Redlion and then...
3,082
has anyone found a successful citect native driver to establish successful comms with a ABB AC500 PLC for modbus on etherne
1,448