I have 20 SLC 500 5/03s

I want to put them on a ethernet network to Citect.

I figure I will have to use use the the 1761-NET-ENI module
I prefer to use a 3rd party module(Data-Linc NET-620) or (Digi One IAP)

Has anyone done this?
 
Thanks

they are on a DH 485 network.

I have used the the NET-ENI modules in the past with little issue But they at end of life and pricey

Plus I am looking of info the ease (or not) of Configuring Citect to communicate the a SLC 500 DF1 port on ethernet
 
The channel 0 port on the SLC5/03, 04 & 05 can be configured as a DF1 full duplex port which is how you configure it when connecting to the NET-ENI and the Net620. With both of these you communicate to the Ethernet port as if it were a SLC5/05 or MicroLogix port. If Citect can connect directly to either one of those via EtherNet/IP TCP you should be able to communicate with it when connected to the SLC5/03. Having said that, my only experience with either one of those is with AB equipment only so there is a possibility that the Citect will have an issue not recognizing the processor. When you connect via RSLinx (using either bridge) the PLC still shows up as a MicroLogix or a SLC5/03, 04 because RSLinx recognizes the PLC even though it’s a non-Ethernet PLC on an Ethernet driver.
 
Yes Citect can communicate to a SLC over Ethernet to the DF1 port using a DigiOne, have done it many times previously. Just use the ABTCP500 driver in Citect.
 
andrewf... thanks

Do I have to run RSLINX as a bridge between Citect & the SLC or does Citect communicate directly to the SLC??
 

Similar Topics

Hello everyone. Could someone please assist me? I am using Citect version 7.2 service pack 5 and Windows 7. I have created a project...
Replies
0
Views
86
Hello, the system we use is Scada 7.5 series. We have usb key activ now we need additional key to make the system work, how do we solve this...
Replies
0
Views
106
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
132
Hello, i've been at this for months now, i tried creating accounts on the aveva website but it seems to never approve my accounts or at least when...
Replies
3
Views
142
Hello, I have a running project on Citect v5.42 and simatic net v6.4 I have created a new spare PC and loaded all software like Citect, station...
Replies
0
Views
89
Back
Top Bottom