I need to test 4 vertical pump motors speed. I need to find a tach sensor for each that I can clamp to the shaft and feed to the PLC.
The shaft speed is 1500 rpm and below, VFD controlled. shaft is around 1.25 inches diameter.
I am open to about anything, I will have the cables for these laying on the ground up to the PLC (contrologix) which is about 50 feet away. As I said, its a temporary test.
Is there a sensor ready built for this or will I have to use a prox sensor and hope there is a keyway or bolt to sense?
I would rather clamp a ringlike device to the shaft tha the sensor can reliably pick up, but my googling has not located such a device.
Ideas?
VFD does have output, I have ordered Ethernet/IP cards to get all the pertenant data from it. But part of this is checking to see if that too is accurate all the time. The pump is not consistent, I suspect its operating right on the egde of its curve and thus becomes a hydraulic issue but I need data to support this before they will bring in the pump engineers. It becomes a design issue (flaw) and so I gotta have all my data right before calling the PE's wrong.
The rear of the shaft is not available on this motor, only the mid part where the coupling and wet seal is located is open.
Copy that. That was the first thing I thought of since we have a handheld one of those, but mounting was problematic. Considering other options, I guess mounting is the least of my problems.
Think I'll need a high speed module for the input pulse?
Both DynaPar and Turck make shaft clamp tachs/encoders. The also have the m12 style connectors avail.
You may not need a high speed input.
1500rpm = 40ms between pulses. If your scantime is low enough you might get away with it.
You also need to make sure that you're not exceeding the maximum input frequency of your digital input, but from memory you can get about 1kHz out of an AB input card, and 1500 pulses per minute is about 25Hz. Take the switching speed of whicever sensor you get into account as well, if it takes 10ms to switch you're going to be pushing the proverbial uphill.
I definitely wouldn't promise it'll work, but if it's for a temporary setup it's definitely worth a shot.
This post on another forum has some detail on a guy doing something similar - he was actually using an encoder and counting pulses from that rather than a sensor, and admittedly he was posting because it wasn't working, but it had worked fine for years before this
Could you possibly just use a hand tach to check your VFD output? If you have already ordered the gear for coms between the PLC and VFD I would compare your VFD's RPM output to that of a hand tach for accuracy. I would have probably just kept it simple and done this before ordering the com equipment.
One of the nice things about a photo prox is distance doesn't have to be exact. I usually just bolted a chunk of unistrut to the frame and used a conduit clamp to hold the switch.
Good Morning , We have a large machine with a number of shafts , and I would like to monitor those to make sure they are constantly...
2,142
Good afternoon, This one may sound crazy. I have a device that is configured to outputs a 0 to 10 volt signal. the scaling is 0 - 0 and 10 -...
1,661
Good morning everyone, This is my first post here. I am beginning my journey on PLC programming and still a really newbie, I want to write a...
1,267
So... Long story short, some of our electricians struggle when asked to measure loops. A clamp on meter resolves this. The Fluke 771 is a great...
22
6,614
I have a boiler with a max steam flow. is there away to Clamp the CV value whenever the Steam output goes over 40000 PPH My PIDe is controlling...
2,088