So I have a tight fitting application which limits me on the components I can choose. I have 4 servo controllers 240v Single Phase and each one of them I would like to fuse the bus supply line. So that gives me 8 total fuses. Well my cabinet which was handed to me and I can't expand the size of (Thanks Mechanical guys) is very tight and I'm questioning whether or not I have to use Class J fuses for these? It's a practice I would typically do but to be honest I don't know why?
Looking for some code or feedback to support the choice of fuse type/class for this situation. Classes M,CC and RK# would be much smaller here. Can anyone offer your support?
What's the fuse rating? 1.25 x .25 would be the smallest - they are 250V and usually go up to 15A. Most common din rail fuse holders for those little guys are in the 8-12A range so verify the holder before you spec the fuse
Looking at using these guys from AutomationDirect.
https://www.automationdirect.com/adc/Videos/Catalog/Circuit_Protection_-z-_Fuses_-z-_Disconnects/Fuses_-a-_Fuse_Holders/Fuse_Holders,_Fuse_Blocks_-a-_Accessories/Class_CC_-a-_Midget_Fuse_Holders_-a-_Accessories_(30A)/EHCC1DU#btn-bar-a
They are Class CC fuses, 30A, 600V.
The fuses are these. https://www.automationdirect.com/adc/Shopping/Catalog/Circuit_Protection_-z-_Fuses_-z-_Disconnects/Fuses_-a-_Fuse_Holders/Current_Limiting_Class_CC/HCLR10
Also Class CC fuses 600VAC rating @10Amp.
I'm satisfied with their specs but im more interested to know if there is a reason to use a specific Class fuse for an application.
The servo controllers you are feeding likely have been listed with the Class J fuses, in which case using anything else would void their UL listing. Class J are fast acting and help electronic power devices pass the necessary SCCR values people look for. Using a different fuse would mean the servos were not tested with them, relegating you to a 5kA SCCR, so installing the system anywhere in an industrial environment would be all but impossible.
Class J fuses and holders come in multiple sizes, the smallest being roughly equivalent to CC fuses in size. Are you in the smallest J that you can use for your amp rating?
Ken
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
117
I'm looking for some clarification if anyone here is familiar with UL698a panels. Panel is out of zone/class'd area. with thermocouples extending...
120
Hi, im facing an issue to change the alarm level into another state in the alarm class configuration in Cimplicity. Im trying to change the...
473
Hi - I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing...
985
I'm working on getting a handful of devices hooked up to an EWEB card on an Allen-Bradley 1756 PLC using the Ethernet/IP socket interface, and...
2,050