CLX - Cache Connections in MSG configuration
fpap
Apr 2010
Puerto Madryn
32
Hello everybody,
I am working with a ControlLogix 1756 L63 controller and RIO, with a DHRIO module.
I have a doubt about the Cache Connections checkbox in the Message configuration window (under Communication tab). I know (because I tested it) I have to check that option, otherwise the message is not executed successfully (it generates errors). I have multiple Block Transfer Read and Write blocks, used to configure analog modules over RIO, and to read from and write to. What I really want to know is if there are any problem setting Cache Connections in every Message. Is there a limit?
Thank you in advance
Greetings
Fernando
Actually you can use un-cached MSG instructions with the 1756-DHRIO and Block Transfers, but you cannot mix cached and un-cached messages to the same Block Transfer Module.
In addition, there is an important limit to the number of cached connections that can be supported by the 1756-DHRIO.
As I understand it, there is a limit of 16 cached messages per channel of the 1756-DHRIO module as well as a limit of 32 cached messages on DH+ or RIO per ControlLogix CPU.
The 32-message limit is a per-controller limit.
This limits the number of Block Transfer devices that can be successfully used with a ControlLogix and the 1756-DHRIO scanner module.
The 1756-RIO is a special module that was released about 2 years ago and has an unlimited RIO Block Transfer capacity. I have used it successfully to convert large PLC-5 and PLC-3 systems to ControlLogix.
I recommend two excellent RA TechConnect documents that discuss the capacity of the 1756DHRIO in detail:
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/37099
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/41853
Thank you very much Ken! Your explanation was very clear! I was sending an uncached message to an analog input module, in order to configure it, and I was trying to read values by a cached message. That is not valid, as you said, you can't send cached and uncached messages to the same module, they all will fail.
So I will have to choose which modules will have cached connections and which not.
Thank you again!
Best regards
Fernando
Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
211
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
446
What's the best way to move a tag value from the panelview+7 to the clx plc. We display amps from a power meter on the panelview screen, read in...
409
I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5. It has multiple RIO...
639
We have two sites that are stranded with no line of site, they are handled by phone/modem with a chain that includes: Stranded site (client)...
927
