CLX DH+ fault
geniusintraining
Jun 2005
SC
8,287
Hey guys,
I have a 1756-DHRIO/B, that is faulted "bad class" ???
From the help file "16#0005 An incompatibility exists between the software and the module."
But I can't find much of anything else, it looks like channel A is the fault B is ok
I have a similar problem right now and I hope someone can point me to the right direction.
I'm doing a DH+ MSG (array of 25 INTs)from a 1756-L63 thru 1756-DHRIO to a PLC5-40/V Ch1A (Ch1B in RIO mode, 230K).
The 1756-DHRIO is set to ChA 230K so ChB is disabled. The MSG executes with no error and the data is being received at the PLC5. The CLX IO config however, shows an IO Faulted error (Code 16#0005) Connection Request Error. Bad Class (see attached screen captures). As per the Rockwell knowledgebase it is Switch 1 and 6 but I tried putting Sw6 (ChB) in different positions and same result. Sw1 (ChA) is in position 3, DH+ 230K. Can't find anything else in the KB or the net. Any help is appreciated. Thx.
If you put switch S1 to pos 3 then you set Channel 1A DH+ to 230kbaud
With 230K DH+ channel 1B will be automatically disabled
If DHRIO does not have RIO (1B) then you will see this error in I/O configuration.
So rule is simple delete DHRIO module from I/O configuration, it should not be there - valid for all comm modules
Also
Even S1 is set to pos 3, S6 must be in pos 0-2 - all other selections are invalid and will fault the module
Contr_Conn,
Thanks for the tip; removed the DHRIO from the IO tree and the fault indication disappeared.
Now, how do I monitor if there is actually a fault in the DHRIO module? I was trying to search for any CIP messaging example in the RA KB but so far found nothing.
GSV wont work as it requires the module to be in IO tree. Thx in advance for any help.
Hi, I have an issue with AB Redundant PLC which was running perfectly for several years and all of a sudden both PLC was showing fault and...
2,691
I have a controller issue I think. 1756-L63 Using RSL5000 v20.05 I can verify a project and download it, do online edits and monitor fine...
2,811
I need a little help again guys. I'm trying to understand how on this CLX program the alarm messaging is being manage. I'm trying to add a new...
1,188
I have added a Generic Ethernet Module to a Control Logix processor. Where can I find the fault code in the Control Logix that shows I have lost...
4,217
First time poster so I apologize in advance if this topic has been discussed before. I did several searches but came up empty. I am trying to...
4,356
