CLX DHRIO to PLC 5/40 via DH+
jschapansky
Apr 2008
Kamloops
32
Hello,
I have had a network similar to this working in the past at a different jobsite, but am unable to get this to work.
I am trying to connect the CLX to my PLC 5/40 with a DHRIO card. I have the DHRIO connected to the PLC5 with a terminating resistor on both ends. I have DHRIO channel A set to 57.6Kbaud DH+ and it is node 2. The PLC5 channel 1A is enabled in the program and set to the same Baud rate and node 1.
Problem is.. the DHRIO says "Only Node" and I can only see the DHRIO in Linx.
I checked the cable, its not shorted or open. The round DH+ port on the PLC5 works fine.
any suggestions?
Try swapping the blue and clear wires; I believe that "Data 1" and "Data 2" are physically inverted on the PLC-5 versus the DHRIO module (on the DHRIO, Data 2 is on top).
Yup, that worked! Thanks
I swear i always work on something for days before i post here and within hours, usually the problem is solved! I love this website
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
3,375
Can i terminate(put resistor in terminal of channel a)the blue hose of an existing plc5 dh+ network to a new 1756-dhrio in new clx rack without...
2,738
I'm working on a project where a Control Logix PLC will be upgraded to become a redundant PLC. The CPU Rack will be duplicated and has two...
1,846
Hello All, I am doing a PLC5 to CLX conversion and asking if someone can point me in the right direction. Let me prefix this by saying that my...
1,576
Chassis 1 L61 PLC FRM 16 ENBT Module CNB Module Chassis 2 DHRIO/D DH+ Channel 1 and 2 CNB Module Control net is working fine DHRIO does not...
4,108