(Code 16#0113) Module connection limit exceeded

PainAmplifier

Member
Join Date
Jan 2012
Location
Monterrey
Posts
8
Hello,

I have a problem with control logix. Using "1756 controller", 1 "1756EN2T" ethernet module, and 2 "1756CNB/E" controlNet modules. I have control net Network with 21 "1794 ACN15/D" modules. Each module have flex I/O's digital inputs, digital outputs, analog etc... 1794IB32...etc...OK now problem is: on some modules I have fault: (Code 16#0113) Module connection limit exceeded. In help I cannot to much understand what is it. Can anyone explain little bit what is this fault and how to fix it please.!
 
Is this a new system?
Have you recently added nodes to an existing functional system?
Have you scheduled the network after the new system's power-up or after adding to it?
The 1756-CNB bridges support a maximum of 64 connections, however the recommended connection usage is less than 48.
You might have to add another CNet bridge to your system and split the existing Flex I/O remote racks, or add suplementary CNet 1794 comms modules in order to accommodate your system's I/O requirements. Remote Analog Flex I/O is a very inefficient (however cost effective!)way to transfer data since too many of the allowable CPU connections are used up for Status/Configuration purposes.
I would personally choose 1756 hardware (comms bridges, I/O modules)when remote controlling extensive analog I/O.
 
It is a new system just powered up, Has a lot of flex I/O, but only few of them has that fault, I don't understand why some has that fault, and other not. I don't se any significant difference between them. OK but when you say max 64 connection, what exatly mean a "connection" one connection one module or one connection one input, I don't exatcly know what connection means?
 
I put PowerFlex 700 drives on a controlnet network, and after 18 drives, I started losing drives intermittently. I was needing to put 20 drives on the network, but ended up having to add an extra card.
 

Similar Topics

Hello I am working on a furnace, it has a decent amount of I/O. I've tried to add some kind of recorder to my system but im getting this message...
Replies
11
Views
7,587
I am trying to communicate with an Acromag 951EN-6112. I have a Compactlogix 1769-L36ERM I have loaded the EDS file for the acromag I have...
Replies
2
Views
1,239
Hi! I want to understand this code, who does is word. IF #"Sample timer".Q =1 THEN FOR #Ic := 1 TO 16 DO IF ((#Ic + 1) < 17) THEN //<...
Replies
7
Views
153
I'm working on learning OOP coding for TwinCat 3. I'd like to transfer and optimize the code my company has from AB Studio 5000 to ST TwinCat 3...
Replies
1
Views
101
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
174
Back
Top Bottom