Codesys Raspberry PI Ethernet/IP 1734-Aent
Cgarcia
Aug 2020
Ontario
Hello everyone,
I'm currently working on a project where I have the RPi set up as an Adapter with Codesys and the Allen-Bradley PLC as Scanner. Both instances show a connection with no communication issues but none of them register any IO change.
(Please check attached images)
As you can see, I have an output of 124 DINT(32 bits) and 1 DINT as input on the AB side and 124 Input DWORD(32 bits) modules and 1 DWORD Output on the RPi side. But as I mentioned before, I can't see any IO communication.
Any help would be really appreciated!
Thanks a lot! :site:
Thanks very much for posting those details and screenshots (and again, welcome to the PLCTalk Forum community !).
Since all the connections appear to be in "Running" mode, that suggests that data really is being transferred between controllers, and I'll bet that Wireshark would show that.
One thing that tripped me up when I first started experimenting with CoDeSys and networked devices is that the tags mapped to each I/O module device don't show their values in CoDeSys until they are acted on by some other logic in the controller.
Write a simple LAD or ST routine to copy some of the Input data from the mapped tags to another set of tags, then put a value in on the ControlLogix side, and see if it shows up in your CoDeSys tag monitor or LAD/ST view.
Thanks for the welcome and help Ken.
As you can see on the following image, I have the IO already mapped but I don't see any communication. I also have other tags that should be reading the AB PLC Date and time but they are not updating either.
All of this I have it on a webvisu that it's not getting any variables. Any other ideas? I have tried all I can imagine with no luck.
I don't know if this is important but the adapter itself wasn't working. I had to setup an scanner with no modules to get it going. But the scanner doesn't have any kind of configuration.
Thanks once again!
Did you try to set the following option to always update variables in bus task?
Hello Cgarcia:
Below is a screenshot of CompactLogix communicating with the Codesys EtherNet/IP adapter. This is very straight-forward. I hope this helps.
Cgarcia,
I have read about users claiming you had to install an empty Scanner object alongside the Adapter object in CoDeSys, but that is not necessary.
If you can ZIP and attach (or I'll send you an e-mail as a Private Message), I'd like to see the CoDeSys project itself.
This may be as simple as the 32-bit data header or trying to use the direct %I and %O addresses instead of mapped tags.
I have a couple of Raspberry Pi 3 B+ units to use as test platforms, and a 1756-L61 with 1756-ENBT.
Anyone have any experience getting a Raspberry Pi with CoDeSys to connect to a 1734-AENTR Ser. B, or any AENT? It's using a IB4 input, and a OB8E...
4,078
Hello, everyone. My supervisor recently purchased a Raspberry Pi and was curious about loading Codesys onto it for practice in the different...
8,163
Not sure if product alerts are allowed but 3S has officially released Codesys for the Raspberry Pi. 35 euros per license...
16,323
Hello to all, can you please provide an example of obtaining a current working directory as a string in CodeSys? For example, during starting the...
202
Hello to all, I'm just starting with using CodeSys. Immediately, I have noticed that Codesys doesn't use data blocks like for example S7 does...