Comm issues
drewcrew6
Apr 2002
allentown, Pa
418
Alright I have 4 micrologix 1500 (nodes 2,3,4,and 5). Going to (4) 1761 net-aic. Also another net-aic going to a 5/04. Hook up to dh+ , go pass through and everthing looks and runs fine. Remove power to a micrologix and my messaging starts to return incorrect values. The values get worse as you power down more micrologix. There are message writes in the 5/04 to each micro. There are reads and writes in each micro going to the 5/04. All parameters have been triple checked in all the message blocks.
It also seems that if a micro messaging "freezes" the incorrect values start to appear.
Any Ideas. This is driving me nuts!!!!!
I added logic in the micro's to kick start the messaging if it stalls for more then 5 seconds.
I have not lengthed the time between messages in the 5/04 because when it works it works fine. It'll run for days before the values get weird and we kick start the messaging again, that why I added kick start logic.
Occasionally a micro has to be powered down for servicing the unit so I need a resolution but I out of ideas.
Enough rambling.
HELP!!!!!
Drewcrew6
... my messaging starts to return incorrect values.
Do you mean the messaging initiated in the SLC-5/04, or in the MicroLogix ?
This points to the issue being in your SLC-5/04 messaging application logic, not on the network. It's extremely unlikely that the actual message data is getting corrupted and yet the MSG blocks are successfully completing (which indicates a correct CRC error check on the packet).
What does your SLC-5/04 message logic do when a message to a MicroLogix fails ? Does it go on to the next MicroLogix, or does it re-try ? If it skips over the node to which messaging failed, how long does it wait before it tries to message to that node again ?
I'm also not sure why you have MSG reads in the Micro1500 and MSG writes in the SLC-5/04, unless they're for data that changes on an event, rather than periodically. What's the theory behind your communication strategy ?
message problems
I am not sure exactly what is happening, but you may be getting a buffer overflow problem especially if relying on timers for your MSG blocks when 1 processor shuts down.
There has been a lot of discussion about MSG blocks here, do a search on MSG or message and you can find some good examples.
The message writes in the 5/04 are timed and sequential. When a micro is powered down the messaging errors.
In the micro's the read updates certain values, one value is okay to write which triggers the write message.
I don't have the code at home so monday night when I go back in I will check how long the timer is for the 5/04 messaging.
Drewcrew6
Hello all, new here. I have 16 Powerflex 40’s that I am converting from DeviceNET to Ethernet. I changed all of the Comm modules to 22-COMM-E and...
1,133
I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
2,449
Hello all. Been reading for a long time, 1st real post. AB was unable to help me beyond "Yeah, that's old, we think you should upgrade..." which...
2,410
Does anyone here on the forums have any experience with Solexy I.S. ethernet isolators? The model we are using is BXF3S010N0018. Issue we're...
1,835
i have a R-J3iB Contoller with a M16ib Robot. When connecting to the controller with my laptop which is windows 10 and going through RSLinx 4.11...
1,644