Communication bet S7-400 and PC using NI opc server

prasad.shukre

Member
Join Date
Mar 2009
Location
surat
Posts
1
Hi All,

I am developing a SCADA for siemens S7-400( 412.2) plc. For this project i used NI opc server to build scada. My problem is that NI opc server support for serial, ethernet or modem. But siemens stopped their production for MPI serial adapter. IN NI opc server i don't have any settings to configure USB MPI adapter. How will i configure USB MPI adapter in NI opc server? Is siemens povide some drivers which support USB for NI opc Server?? Or there are another hardware (except Ethernet module)which can i use??


Prasad
 
There is CP5611 (PCI), CP5621 (PCI express) and CP5711 (USB).
They all require that you use Simatic Softnet, and not the NI OPC server. The common Siemens PC Adapter USB will not work with Simatic Softnet.

There are also 3rd party Ethernet/MPI adapters. Look for Deltalogic and IBH. I dont know if NI will work with any of these. If not, they have their own OPC servers.

Since the NI software supports ethernet, then you could add a CP443-1 to the S7-400 rack. Expensive though.
 

Similar Topics

problem in a communication that lost bet. S5 135U (ALARM S3964RDDE SERVER) & In Touch Hi all experts and members ...
Replies
0
Views
2,132
Hello every one hope all are enjoying. I have an issue to connect omron NS10 HMI with CJ1M-CPU11 ETN plc I have made all required setting as...
Replies
8
Views
94
Hello guys, I'm working with Emerson's ControlWave Micro and I need to configurate the controller as a DNP3 outstation. It shows me error -8002...
Replies
0
Views
30
So i need to communicate my VFD (LS Electric iS7) with XGL PMEB module i successfully set the gsd file now i cant figure out how the data works...
Replies
0
Views
72
Greetings. I currently have several systems in operation mainly using Aromat PLCs and Beijer Exter HMIs. The HMIs email to VText.com to send us...
Replies
0
Views
66
Back
Top Bottom