hi mates, i want to connect my twido with a m340
i use modbus protocol RS-485
my cable's properties are:
twido mini Din - m340 RJ-45
1 - 4
2 - 5
7 - 8
8 - 7
and modbus parametres are:
-parity Even
-rtu
-9600 bauds
-stop bit 1
and here is serial port of twido
and m340's port
am i doing something wrong??
because it doesnt work....
any ideas??
Two things - simplify to start and use just two wires.
Per M340 documentation:
The pins used by the RS 485 serial link are as follows:
z Pin 4: D1 signal
z Pin 5: D0 signal
Pins 7 and 8 are used solely to supply power to human-machine interfaces via the
serial link
Do you need the power pins? If not, disconnect them.
So I would try:
1 - 4
2 - 5
if this doesn't work, swap one pair:
1 - 5
2 - 4
Failing that, I set up a PC with rS485 adapter and make sure each one works there directly to the PC.
If you use Twido's programming port, then you have to connect pin5 (DPT) to 7 (0V). If you don't connect it to 0v, port is on programming mode and modbus communication won't work.
so, probably
1 - 4
2 - 5
if communication don't work swap A and B signals, as robertkjonesjr wroted.
And disconnect power cables, now you have short circuit from +5V to ground.
Hi! I have a some problem with TWDLCDA24DRF PLC. Does anybody halp me?
If somebody have this PLC, please open the cover and on the bottom layout you can see some transistor. It marked (Q18) on the layout. I want to know the number of this transistor. It is burned in my TWIDO.
so, probably
1 - 4
2 - 5
fantastic Lare!!
it worked perfect, thanks a lot!!!
Hello EveryOne...!!! Please Let me Know if this could be possible..!!! I want to connect twido suite 2.2 and Citect scada over local address of...
1,797
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
119
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
67
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
85
383