Connection of floating level sensor with PLC s7-200 CPU 226

Connect the first wire to that terminal and the other wire to the second terminal...oh and if there's a third wire then connect it to that other terminal...does that help? :)

If you would like other people to help you may need to give more information (manufacturers details/part no. etc). Is it a 2 wire or 3 wire sensor? Is it configured for 0-10V or 4-20mA (or even 0-20mA)? Which analogue expansion module are you trying to connect to?

The more info you provide the more detailed the replies will be. :oops:

Regards,

Rob
 
specification of floating level sensor

>Float type
> Switching voltage: Maximum Voltage: 240 VAC\ 200 VDC.
> Switching Current:2A
>Two wire
>Bottom plate fix and upper plate moving
>works using magnet


 
Sounds like a discrete sensor. How you wire it up depends on how you wired up your PLC. Basically this float switch will operater the same as a pushbutton and will wire to your PLC the same way.

Know this is kind of vague but without more detail it is the best I can do.
 

Similar Topics

I'm having a hard time either remembering or figuring this out. I have a PLC program and the associated HMI program. I know what this means...
Replies
4
Views
118
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
8
Views
273
Hello guys i'm working with an s7 1200 plc with an ET 200S expansion module. The problem is that i can't find the plc when searching in the...
Replies
1
Views
122
I have got an Rockwell PLC 1769-L36ERMS . I have assigned a IP address to it . But every-time I Reboot the PLC it looses Communication to my PC...
Replies
1
Views
114
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
171
Back
Top Bottom