A lot will depend on how sensitive is the pressure rate of change with respect to flow. If the volume of fluid under compression is small then pressure can change too quickly for PLCs. dP/dt=β*Q(t)/V
dP/dt is the rate of pressure change
β is the bulk modulus of the fluid
Q(t) is the flow as a function of time
V is the volume fluid under compression
Another way of look at this is
ΔP=β*ΔV/V
If the volume under compression is 100 cubic inches and 1 cubic inch of fluid is added then the pressure will increase 2000 psi for oil and 3000 psi for water. This means the pump must be able to add fluid at a very controlled and small rates.