I have been tasked to control two PF525 VFDs with at least one PID loop in a duplexing pump scenario. The project pumps water from a lower tank into a tank on top of the lower one, which can then be drained back into the lower one via a hand operated valve. No matter how fast water pumps back into the lower one, the level has to be maintained in the lower tank. The level on the lower tank is monitored with a banner ultrasonic sensor.
I have one working PID loop which calculates how far off the tank level on the lower tank is from my setpoint. I have it tuned to operate how I would like it to but I am struggling incorporating my two VFDs into the project.
How would I be able to control two VFDs (or just one depending on rate of flow) with one (or more if needed) PID loops?
Welcome to the forum!
So if I understand correctly, you are not alternating pumps, but rather using 1 pump for low flow demand and two pumps for high flow demand. Is this correct?
If so, there was a similar scenario presented in a post several months back. A search of the forum posts would be helpful. I'm up to my armpits in alligators presently, so I cannot do much good other than to say the solution involved a bit of an overlap between the two pumps, if I remember correctly. Only one PID loop was used in that solution.
My guess is that with only one pid you an control lower tank level, be careful with valve on upper tank, I would use open and close limit switches on that valve just for security, and in some cases to stop pumping from bottom tank.
Hydraulically, are the pumps in series or parallel? In other words are there two pumps because you have a high static head and need the boost (series) or do you potentially need higher flow rates (parallel). Depending on that answer, this might be very simple.
Hi Everyone, I was wondering if any of you have ever tried to control a load using the internal 24VDC on a Powerflex 525. In an application I've...
2,690
Afternoon all, I'm working on setting up a large excel recipe table for porting updates through the Linx Gateway RTD/DDE function into my recipe...
123
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
521
I'm a Manufacturing Engineer with limited PLC experience and I am doing some research for our Controls Department. Does anyone have experience...
189
Good Evening , I should know more about Solid State Relays . I have a system with 8) 120 vac Vibrators . These Solid State Relays have...
24
2,088