I need suggestions.
I want accumulate operating hours from a simple XIC condition, so I'm thinking a RTO with a 60000 or 3 600 000 preset, 1 or 2 CTU, you catch my drift. The unit can be operating for 1 hours up to 12 months non-stop, if that changes anything. I'm also looking to keep the number of operations on a breaker.
What I'm wondering is how to make sure that I don't lose the count / values on a full PLC download. I'm guessing what you're going to tell me is to make a note of the actual value and put it back after the download, or save / upload values before doing a change, but that is not always possible, and that will be lost anyway if the customer do its own changes later, even if written in the O&M.
So I'm asking if there is another way to try to not lose the values.
I remember I once did something like that with a different brand where I had another PLC on the network at a "higher level", so I had a logic that would give the value back if it was different, or lower, or zero, but this still looks kind of overkill for a stupid accumulated time counter, and more data exchange to set up.
I have the same setup here (PLC at "higher level"), so I could do something like that again, but I'd really prefer not to.
There is also a standalone InTouch HMI on that setup, maybe there is something that could be done using that?
Thanks for your suggestions.
I need suggestions.
I want accumulate operating hours from a simple XIC condition, so I'm thinking a RTO with a 60000 or 3 600 000 preset, 1 or 2 CTU, you catch my drift. The unit can be operating for 1 hours up to 12 months non-stop, if that changes anything. I'm also looking to keep the number of operations on a breaker.
What I'm wondering is how to make sure that I don't lose the count / values on a full PLC download. I'm guessing what you're going to tell me is to make a note of the actual value and put it back after the download, or save / upload values before doing a change, but that is not always possible, and that will be lost anyway if the customer do its own changes later, even if written in the O&M.
So I'm asking if there is another way to try to not lose the values.
I remember I once did something like that with a different brand where I had another PLC on the network at a "higher level", so I had a logic that would give the value back if it was different, or lower, or zero, but this still looks kind of overkill for a stupid accumulated time counter, and more data exchange to set up.
I have the same setup here (PLC at "higher level"), so I could do something like that again, but I'd really prefer not to.
There is also a standalone InTouch HMI on that setup, maybe there is something that could be done using that?
Thanks for your suggestions.