ControlLogix Date/Time setting differs from Date_Time Tag values
Marius ZA
Feb 2011
Pretoria
Greetings
In our plant we use a ControlLogix5563 as our main data handling PLC. Recently I noticed that the controller date/time setting differs from the Date_Time tag which we update by GSV instruction.
The controller time and DateTime tag differs by 2 hours.
The rest of the tag datatype fields are correct. Just the hours differ.
The Date_Time Tag is structured as follows:
Date_Time
  • Date_Time.Year
  • Date_Time.Month
  • Date_Time.Day
  • Date_Time.Hour
  • Date_Time.Minute
  • Date_Time.Second
  • Date_Time.Microseconds
This should be correct.
I am not sure what caused the issue.
For a temp fix I simply adjusted the controller time by 2 hours and the Date_Time tag updated to the correct actual time.
How can I fix this nuisance? :mad: What caused this?
Your help is appreciated.
-Marius ZA
Don't use the DateTime attribute in the GSV.
Use the LOCALDateTime attribute.
You are reading the GMT time, without compensating for your local time zone.
I agree with the change and made it - makes sense.
Yet the controller date and time is now at 2:26 PM whereas the LocalDateTime to Dest: Date_Time.Hour is currently at 12
No CST master settings and no daylight saving activated.
The Time Zone setting is correct.
That is odd... if the time zone is properly set, the GSV LocalDateTime should always return the same time as displayed in the controller dialog.
Have you tried 'Set date and time from workstation'? (assuming of course, the workstation time and zone are correct.
All of our Logix PAC's are synced off of our site master time server with the Logix Clock Update tool every day, but all of them (that I have just browsed) agree that the controller time is the same as the GSV LocalDateTime.
hello i had a 1756-l61 with firmware ver 13.24. a solid red made the processor not functioning. i ordered a processor that came with firmware ver...
3,828
I am working on a project where i need to communicate Markem-Imaje SmartDate X40 with Allen Bradley ControlLogix PLC over Ethernet. The...
1,446
1,358
Hi all, I have a Controllogix PLC with an L73 processor (v20) and an M02AS module. I'm very familiar with the HYD02 CLX module but am running...
7,176
what keeps setting my local PLC time 8 hours back? even when I hit the "set time to workstation", it immediately gets overwritten.:confused:
5,563