ControlLogix SLC Typed Read/Write SLC 505
Just wanted to circle back and close the loop on this.
Replaced the older SLC with 10Mb Half duplex ethernet with a Series C with FRN 13. This was about 36 hours ago at this point. 0 MSG errors since. Max time for both Read and Write in that 36 hours is 38ms . Overall Timer is much shorter (just over 100ms comms round trip). So basically the older SLC was not capable of this Series C appears to be.
Thanks for all the great the help.
Brand new L72 processor. 1756 DHRIO card in local slot 15 we have DH+ running to a SLC 5/04 grabbing a few integer files. Well since this new...
2,967
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
183
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
102
Hi all, if I remember correctly, there is some way in a ControlLogix (or CompactLogix) where you can sort of map tags into SLC addressing format...
1,194
A new Forum member resurrected an old post with a variation that I think should be done in a new thread to get the best attention and advice...