I've the following system at our plant
A ControlLogix 1756-L55, with Eight 1756-CNB/D (Control Net Bridge Modules) at eight remote locations. This system also has 8 PowerPlus II 1336F VFDs using the scanport. All of it is in a control net configuration.
We recently had a power outage at our plant. After that, only those I/O modules installed on the main rack, in which the Logix 5555 processor is installed, are functioning, the rest of them are not.
Physically, a green light is flashing on the I/O modules. In RSLogix, their internal state appears as "Unconnected" in the Module info.
I am getting the following error in the 1756-CNB/D module, which is installed in the main rack (the one with the Logix processor),
"connection request error: controlnet configuration in controller does not match configuration in bridge"
(Code 16#0305).
All the CNB modules, I/O modules and the VFDs are appearing in RSLogix with the yello exclaimation mark. However, I am able to check the parameters out of the drives using AB DriveExecutive without a problem.
Any ideas?
To all, This is brownfield system modification of PLC-5/80C system, redundant processors with remote Flex I/O. The process is continuous (oil and...
1,449
Hi. I have an issue with the Control Net module 1756-CN2R that keeps generating 'Duplicate Node Detected' (DND) in random ControNet nodes in the...
2,070
I’ve mentioned bit of this before, http://www.plctalk.net/qanda/showthread.php?t=68356 Its a bit long Last year I inherited a system...
4,200
Hi guys I got a problem when I try to update a COntrolNet system, they use a 1756 CN2/B in the local chassis, I am going to add another 2...
3,042
We have installed a control net network on which we have 3 nos Flex Logix controllers and 2 nos Workstations (PC). The problem is that on one PC...
2,029