You have to remember that PLC5s are using Octal Addressing; this is the reason a PLC5 16-bit word ranges are 1-7 and 10-17.
The SLC platform uses decimal addressing hence up until bit 7 (inclusive) the addressing is identical, however, PLC5 X:Y/10 becomes SLC x:y/8, PLC5 X:Y/11 - SLC x:y/9 and so on until PLC5 X:Y/17 becomes SLC x:y/15; you might need to relabel the field wiring though...:D
one of the biggest issues in making this type of conversion is that the PLC-5 platform (the original) uses OCTAL addressing for its Inputs and Outputs ... but ... the SLC-500 platform numbers its Inputs and Outputs using DECIMAL ...
the best way that I've found to handle this is to make an Excel spreadsheet and show the original PLC-5 addressing in one column - and then fill in the next column with the corresponding addresses for the SLC-500 system ... if you go through it systematically, you'll start to see the pattern ...
I wish I had more time to help – but I'm swamped with work right now ... I'm sure some of the other forum members will be glad to chip in – but you'll probably have to be specific with exactly which addresses are giving you a problem ...
and to answer your specific question:
and will my program recognize the proper address the 16th node?
only if YOU (the programmer) properly convert the addresses ...
analogy: suppose that the Post Office goes down your street and reassigns some of the house numbers ... question: will the mail still go to the proper recipients? ... answer: only if someone goes out and repaints the numbers on the affected mailboxes – to match the newly assigned house numbers ... that "someone" will be YOU – the programmer ...
good luck with your project ...
thanks guys, i caught it about half way through the program change over... just have to go back.. and re do all of them..
one more thing i must ask though is, i have all the addresses changed and i am getting a major fault on slot one (the 1747-sn) when i attempt to put the processor into run mode. rs logix says that with my version i am unable to use the block transfer read and block transfer write instructions... i read that i need those to be able to communicate with where the RIO module stores the data.. am i wrong in this? i feel like im so close.. yet could be so far away
where are the Block Transfers that were giving you trouble? ...
you've only got a 4 slot chassis ("rack") with only the Scanner module in it? ...
My version of rslogix does not allow me.to select btr or btw... and yes.. the rack only.has a scanner and CPU... all of the io is flex io with a 1747-asb module.. baud rate is the same and proper resisor is in place.. i selected the g file length of 5 and selected a"whole rack" in advanced config
I would look hard a long for the old offline file or if at all possible try to contact the original
programmer. That's a big program to add comments to.
Hello everybody, Could you please confirm if there is any automatic or semi-automatic tool to convert projects: 1. Convert a PLC5 project (.RSP)...
1,630
Hello, could someone kindly convert the attached RSP files that are currently used for SLC 5 PLC into PDF please
563
I currently need to download about 400,000 bits of RSLogix 5 from four Allen Bradley SLC 500 to a flash stick for printing or viewing. Does anyone...
4,034
We recently purchased a machine with a PLC5 controller, never used this before, we are all SLC. Can someone convert this AB program to pdf for...
2,266
Hello all, I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI...
112