Hello!

I work for a company which has a power plant in Bangladesh.

The plant has 7 Siemens 300 plc's, which are connected to a computer on Profibus with s7 communication. The pc has a CP 5613 in one of the slots on the motherboard. It has Simatic NET installed, Net communicates with the driver in the scada application

This week they called because they got error messages and they said that there are no lights on, on the CP card. They took it out of the pc, put it back in and then it worked for some minutes before it went out again.

The messages they got were the following:

1. The software version doesn’t fit with the hardware version of the CP5613_5614


2. Please send the internal CP data to the SIMATIC NET hotline


3. The internal CP data is written to the file: C:\Program Files\SIMATICNET\CP5613_5614 \Logfiles\EXCP_CP1.bin!


They restarted the computer and got the following messages:

1. Defect(ICE) CP5613_5614 hardware


2. FW nitch gestarted->timeout


Have anybody seen these messages before?
To me it is obviuos that either the CP card or the slot on the motherboard is damadged...



Thanks alot for any answers (y)

regards
Andreas
 
CP5613 cards

I use CP5613 cards with Siemens S7-400 PLC's.
There are at least 2 different cards CP5613 and CP5613 (A2) and they require different simatic net software.
I have several of each type running in factories in India and have had a few problems as follows.
1. CP5613 die sometimes.
2. CP5613 don't seem to like high temperatures.
3. Using Profibus cables (thick and stiff) the cards are sometimes pushed partly out of their PC slot.
4. Some PC motherboards are very badly supported and deflect significantly when the card is installed such that proper contact is not made by all edge connector circuits. I have had to use a rolled up plastic bag between the motherboard and steel pc bottom to hold the motherboard up.
 

Similar Topics

Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
72
Hi, Has anyone had any experience of running any SCADA software off of a Compact Flash card? If it does work okay are there any disadvantages...
Replies
3
Views
3,067
G
Hi! I have to comunicate via PROFIBUS with S7 protocol or DP, the applicom card PC1500PFB and PLC siemens S7 CPU313C-2DP. The cable that i have...
Replies
1
Views
15,441
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
89
Hi everyone. I'm trying to read values from a Loadcell with a 2080-TC card. I know the 2080-TC is a thermocouple card but it reads millivolts that...
Replies
6
Views
113
Back
Top Bottom