CTU reset question
Use the CLR instruction on the CTU ACC. This will leave the CU bit set and reset the CTU ACC to 0.
XIC CTU.DN CLR CTU.ACC
Diagnosing the process, one scan at a time; see images below.
.ACC /DN /CU Trigger
(1) 2 0 0 0 Logging starts, ~5ms before count from 2 to 3
(1a) 2 0 0 0 Logging scans over ~5ms until trigger becomes 1
(2) 2 0 0 1 Scan of trigger rising edge and before count;
/CU is 0 while trigger is 1 => rising edge
(3) 3 1 1 1 Scan of trigger rising edge and after count;
count (.ACC) is 3 = .PREset so /DN is 1;
RESet will occur on last rung of this scan
(4) 0 0 0 1 Scan after trigger rising edge and before count;
RESet has assigned 0 to .ACC and 0s to all status bits,
/DN and /CU specifically are now 0s
(5) 1 0 1 1 Scan after trigger rising edge and after count;
since /CU was RESet to 0, trigger value of 1
is detected as another rising edge on this scan,
even though trigger was 1 on last scan
(5a) 1 0 1 1 Subsequent scans over the next ~100ms; no change
Tried this also......same result.
Hmm, maybe Logix 5000 is different from MicroLogix:
(6) 0 1 1 1 Scan after trigger rising edge and before count;
CLeaR has assigned 0 to .ACC, but all status bits are unchanged,
/DN and /CU specifically are still 1s
(7) 1 0 1 1 Scan after trigger rising edge and after count;
count (.ACC) is still 0 i.e. there has been no "false count" to 1
because /CU is still 1;
/DN has become 0 since .ACC is less than .PRE.
(7a) 1 0 1 1 Subsequent scans over the next ~100ms; no change
Hi all, I'm newbie here to plctalk! I writing a PLC programm in ladder where I put an output bit to zero during 9s and the same output bit to one...
6,938
Hi, I need to use my CV value from my CTU. if CV = 1 : Red light turns ons if CV = 2 : Green light turns ons, but red goed out if CV = 3 ...
310
Hi, I am confused regarding TIA portal and counters. I use CTU. I wish to have one counter counting 0-10. When it reaches 10 is shall increase...
23
3,266
This counter is counting when bits_from_traypacker is true (messaging from other machine, this is the servo cycle). After counting 3 it should...
3,315
For a week now, my coworker and I have been troubleshooting a machine which has been displaying some crazy behavior. HMI values were changing on...
19
4,309