I'm attempting to control a FC302 with a devicenet comms card. I'm set up in the parameters for ODVA and map option 21/71.
I know that my devicenet card, a 1756-DNB, is picking up some data from the drive at Mac ID 48. If I run the drive in hand, I see the RPMs change. The discrete values don't appear to be changing (I see drive ready and drive starting up(??)). And the commands I'm sending (Run forward, Dnet control enable, and Dnet Speed Reference enable) are not moving the drive in Auto.
Any pointers would be fantastic. Danfoss has a Devicenet guy, but apparently he's out on medical leave.
Regards,
Eric
Have you set up the right values in the parameters 8.50 and forward until 8.91. in the manual i se you choose where your commands Start/stop is from a digital input or fieldbus
Jonas.
I set those all to be bus controlled.
I believe I have found my issue, I was set up to send two 16 bit registers for the commands rather than a single concatenated 32 bit register. Similar issue on the inputs.
Hi everyone, I would like to use Micro 850 to control DF FC 102. I adready connect Danfoss fc 102 VFD ( it can run the motor) to Micro 850 by...
1,938
Hello, Has anyone used Danfoss MIDI VLT VFDs over Ethernet with RSLogix 5000 ? We will be using them and i am trying to figure out how to...
1,264
To execute MODWR and MODRD instruction of Delta PLC, I need address of register in VLT 2800 but I cannot figure out. Can any body help me? I want...
7,083
I need to control a FC51 Danfoss VFD with LS PLC. I need to start, stop & jog the drives. I have set all the parameters as per manual for Modbus...
5,149
  • Poll
:furi::hand::smas:I HAVE TO INSTALL A DANFOSS VFD VLT2800 SERIES TO CONTROL THE SPEED OF FEED WATER PUMP TO MAINT THE 5 BAR PRESSURE IN LINE. MY...
5,177