DC drive output voltage beyond rating
unsaint32
Oct 2012
minneapolis
365
Our DC drive L1 and L2 got shorted due to bad motor. We didn't have an exact replacement of the DC drive. So we are using another DC drive that has the same input voltage rating (120v)and same output voltage is rating (0 - 90 vdc). But when we hook up to the motor (no load) the motor seems to spin too fast, and the drive actually produces 145vdc. The speed pod, Accel & decel settings don't make any difference. Why is the output voltage so high?
A DC drive is a simple amplifier. If the speed reference is 0v the output should be 0v, assuming the minimum speed is set to 0 as well.
If not, the drive is bad.
Try disconnecting the pot completely. Turn the IR Comp and Min Speed all the way down. If the output is not ~ 0, then the drive is bad.
There's no 'current mode' on DC drives, is there?
I remember there being a current mode on some of the older Vehicle motor controllers, where you can sort of test the controller with a smaller motor, but the throttle signal is *VERY* sensitive.
Another question - is it possible that you are connected to the DC bus or Inductor terminals instead of the output terminals? That will also give you no throttle response. Some of our smaller DC drives had ... interesting .. terminal labels. It was not obvious what the output was. We actually connected a motor to the inductor terminals once and it took us a while to figure out. I don't remember the symptoms, but the speed reference did not operate very well.
Motor - permanent magnet or field?
If you have field windings, I would check that the field is getting full field voltage (from your description, I would assume 90Vdc). To overspeed a DC motor, you weaken (or reduce) the field, so a bad connection or low field voltage would cause your motor to overspeed. I would measure voltage directly at the motor.
Hi Experts! I'm trying to control a solenoid valve (don't have part number, but I've been told its a 24V DC 30 watt coil) with a PLC output card...
6,612
Hello I need to control a Sew Eurodrive MDX61b position (HI and LO) from a PLC S7-314-2DP with Ipos and I don't understand how to use the strong...
1,577
Hello, I have a drive allen bradley powerflex70 that works normal it shows that it has start and frequency variation but there is no output 0...
2,120
Good Evening , I have a Powerflex drive that has been running steady at about 39 Hz for years , but is beginning to swing 39.6 Hz , 40.5...
2,914
Good Morning , I am working on a project with some PowerFlex 525 drives. I am using CompactLogix 1769-L18. I took notice that the tags that...
23
22,522