I would like to know if it is possible to view a DeviceNet network through the Data highway. I am running RSLinx Pro looking through an Ethernet gateway to a backplane into the data highway plus. The DeviceNet network on the machine is at a very remote part of the plant.
If the Devicenet network is on a Logix 5000 platform processor you can just tunnel through the backplane from the DH+ card to the Devicenet Scanner card. If not you can set up a pass-thru driver in RSLinx. Under configure drivers select the Devicent drivers option. A new window will pop up asking you to select the catalog number of the Devicenet scanner you want to connect to. Afterwards a the RSLinx who active window pops up and you just need to select the comm path to your scanner card.
If you are connected to a SLC 5/04, a connection can be made via the processor-back plane to the SDN card to get to devices its connected to. Warning, for accessing large parameter sets such as in a A-B Ultra 3000, its very slow to upload and download.
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
25
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
85
Hi, I am looking to migrate some of our Electronic Overloads off of a Troublesome Devicenet Segment. Is there any documentation confirming the...
127
We've run into an old system that we are upgrading which is still running Steeplechase with Citect using Devicenet to Wago. I had some experience...
161
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
148