DH+ speed using DHRIO
pheel
Aug 2006
Montreal
Hi everyone,
I have look in the AB manual but I haven't found the answer to my question.
Does the Allen-Bradley DHRIO module can bridge between a 57.6Kbps network and a 115Kbps network ?
It seems obvious for me that the answer is yes, but before shutting down the network to do the changes, I would like to have some inputs :)
thanks
pheel
I don't have the manual in hand, but I am thinking you would need two DHRIO's. I think when you select the high speed you only get one channel out of a DHRIO. I am sure some can verify this.
If I wanted to know, I would read the manual. But that's just me.
RSL
RSL
well, I'll have a look again in the manual. I even talked to Rockwell this morning and they were not sure. They told me to try and see but I might need a second module.
RSL, I too read the manual when I need information but sometime it's not clear and forum are a nice place to look for people that have already had the experience with the situation.
pheel
I've never actually seen a DH+ network running at 115.4 kb/s. It's a valid selection, and I've run RIO networks at that speed, but usually I only see low speed (57.6 kb/s) and high speed (230.4 kb/s) DH+ networks.
The 1756-DHRIO module added support for 115.2 kb/s dual-channel operation and 230.4 kb/s single channel operation in the Series C hardware, firmware version 5.03. See Rockwell Knowledgebase document G53455026 for the switch settings.
The 1756-DHRIO does disable the second channel if 230.4 kb/s is selected as the DH+ speed. This is only a valid selection for Series C and D of the module hardware.
Is the idea that you were planning to increase the speed of one of your DH+ networks to 115.2 from 57.6 ?
Yes, my customer have 2 57.6 DH+ linked with a DHRIO. They have some problems with one of the 2 networks. Rockwell will be there this friday to do a complete analysis of the situation.
I'm planning to propose a speed increase of their networks. I was thinking of modifying one network at a time. That is why I was asking if one DHRIO module could bridge between a 57.6 and 115.2.
I'm aware of the limitation of high speed 230k that disable the second channel on the DHRIO but I haven't seen anything about mixing speed...
Studio 5000 & PF 525, Ethernet Comms, Encoder FB, Using Motor RPM as speed reference I'm trying to figure out how to send a speed reference in...
974
Hi, i need to make: 1- A PLC Program on Omron PLC CP2E-N using high speed counter E6C3-AG5B 360P/R 2M(Absolute) ,to Reject bottles on Conveyor...
908
I am at a loss... I have a pasteurizing system that i need to control product temperature with the speed of the product pump. I currently have a...
2,632
Anyone have a plc program example of speed control on a vfd using high/low level switches. Speed increases for every second the low level is on...
31
10,033
Hello All, I have two bags of two different types of peanuts hanging on a load cell above two separate feeders. I am using Studio 5000 and would...
45
8,918