Diagnose fault
eem_murat
Nov 2009
Istanbul
30
Dear all,
I downloaded program to ET200S and I have below fault on the diagnose. And CPU has below situation:
Module available and o.k.
Error LED (SF)
Error LED (BUS1F)
Thanks for your kindly help
At a quick glance, the PLC gives this message for going into stop.
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
So i would look if there's a SFB20 programmed somewhere.
Maybe the busfault is the cause, but IMHO there's not enough information.
Please post the diagnostic buffer again right after the PLC going into stop without doing anything else so maybe there's more information
The last entry in the diagnostics buffer is for the change from stop to run.
There is nothing about any problems.
Entry 5 with the request for Stop is because of the HW Config change.
Is the IM151-7 CPU configured as slave for a DP master ?
If that is the case, I think that the problem is that the DP master does not connect to the IM151-7.
Hi guys, Some of you may remember me mentioning a backup Profibus connection I have in my project. A quick recap: 1. Existing Profibus...
3,251
Hi all, We have a machine that has about 20 inverters and several other devices attached to it via profibus. Today we had a profibus fault...
6,802
I’m working on getting a Parallel Redundancy Protocol PRP system set up in a lab situation. The L73 PLC is in rack 4. 3 io racks are 1,2,3. I...
770
Hi Everone, I want to know how we Diagnose Digital Input/Output module in S7 300 plC. Cpu 315-2dp Input module SM 321-32DIX24v Output module SM...
2,119
In my WinCC Diagnose log, "RedundancyAgent,Outage detected reason 'NetworkError' ", this statement always logged in my WinCC server I think it...
2,175