difference between the two
mobil1syn
Dec 2018
socal
79
so on the left i have the 1794-IE8H and on the right the 1794-IF8IH. if i understand the manual and all my reading, the IE limits me to run two wire transmitters only and is powered by the card, so no outside power needed. the IF8 allows for 2,3,4 wire devices and needs outside power to run the device.
signals for this job will 4-20ma.
it would appear i left that out.
is my understanding of the difference between the two correct?
It also looks like the 1794-IF8H has isolated channels. It's not clear if the IE does as well but that would be worth looking up in the data sheet or manual.
The 1794-IE8H module accepts up to 8 analog inputs. The inputs are non isolated and will accept current in either of the following two ranges: 4…20 mA or 0…20 mA. The default input range is 0…20 mA. The inputs have both fixed hardware filters and selectable firmware digital filters. The module is used with 1794-TB3G or 1794-TB3GS terminal base with all commons and power terminals interconnected; module is designed to support 2 wires devices only.
The 1794-IF8IH module accepts up to 8 analog inputs. The inputs are isolated and will accept current in either of the following two ranges: 4…20 mA or 0…20 mA. The default input range is 0…20 mA. The inputs have both fixed hardware
filters and selectable firmware digital filters. You can use 1794-IF8IH (isolated) instead, with 1794-TB3, 1794-TB3S; devices supported are 2, 3, 4 wires.
Hello, I have a problem with AO- and AA-Tags. When I use for example the tag AO_Test with the address 200 and type the value 1,2 in, the AA-Tag...
1,416
As per the title. This might seem like a basic question to many, but I'm unclear about the difference between a coil ( ) and an application...
28
4,048
Good Morning , I have 2 Frequency Drive panels to build and commission . It is for 2 pump systems . Just wondering , what is the...
1,975
Hi Experts, Good day! What are the differences between PCS7 SIMATIC Batch and PM Control? Do you have any manual like "Getting Started "...
817
I have a Automation Direct Click Plus that you can buy option CPU slot modules for input/outputs. The slot modules have the options of sinking...
2,838