Dint to Time convertion on Siemens S7-315 CPU with TIA v11
nicknzj
Apr 2012
kampar
17
Hi All,
Can anyone advice and share on the following?
- How can we convert Dint to Time format on S7-315CPU with TIA v11?
- If i need to insert a (TON)timer setpoint from HMI,how can i convert the msec to Hr,Min,Sec and finally the timer will display in countdown mode on the HMI.
Thanks and Regards
in SCL you can try with this: PT:=dint_to_time(variable)
in LAD and FBD i think there t_conv block that do the same.
as for STL i don't think it's possible.
if you need this a lot try with writing a function in SCL that has var for input and give time as return result.
PS: if using SCL you can go with integer, eg. dint_to_time(int_to_dint(variable))
i wrote a similar function once:
FUNCTION "T_min" : Int
VAR_INPUT
"Time_int" : Struct
"h" : Int;
"min" : Int;
END_STRUCT;
END_VAR
BEGIN
#T_min:=#Time_int.h*60+#Time_int.min;
END_FUNCTION
!!! IMPORTANT: do not forget that Timers have PT in msec, so multiply with right factor if you do not have time in msec already
Thanks Balash,
Im not fomiliar with other programming language than Ladder, can you please generate and share a function block which create by SCL ?
well the code is already written, but do as follows:
1. create new function T_dint, choose SCL for language
2. declare input paramter Time_dint DINT
3. declare function return value as TIME (default is void)
4. write: #T_dint:=dint_to_time(#Time_dint);
that's it
of course if #Time_dint is in minutes then everything has to be multiplied with 60000
EDIT:
or if you have hours, minutes and sec declared as inputs then use this:
#T_dint:=dint_to_time(((#hours*3600) + (#minutes*60) + sec)*1000);
vice versa function would have time as input and hours, minutes, sec as output:
#temp:=time_to_dint(#Time_ET)/1000;
#hours:=#temp/3600;
#minutes:=(#temp-(#hours*3600))/60);
#sec:=(#temp-(#hours*3600)-(#minutes*60));
that would be on the fly...
Hi I am being given several fault words (as a DINT) from a Drive that I am receiving into a Compactlogix L33ER controller. I have a small...
1,148
I am working on a project with a Controllogix 5582 processor using v32 firmware where I will be communicating with a Genset using Modbus TCP. It...
994
Hi! It is always said, that DINT is the most performant datatype in AB plcs. I while ago i made a performance test. Several instructions like ADD...
671
Im trying to use a MSG instruction to get the serial numbers of all addon cards and display the serials on a HMI interface. I have the logic done...
576
Just something I think about when choosing data types in Studio 5000. It seems logical, but I've never looked deeply into the question. When...
1,381