There are dozens of instruments. They are divided roughly into two catagories. The ppb type are usually installed in a pipe and are used for protecting boiler feed water etc. The ppm type are installed directly immersed in aquaculture or wastewater treatment tanks. The ppm types include traditional membrane styles and newer optical styles.
Brands available in the UK include Endress & Hauser, Danfoss, Cerlic, and Royce.
There are two DO (dissolved oxygen) technologies - diffusion and equilibrium.
DO measurement based on the rate of diffusion measure the diffusion of O2 across a membrane. The anode needs to be cleaned, recharged or replaced.
Equilibrium is where the DO measurement based on the partial pressure of O2, and the reading is generally independent of fouling and the anode is not consumed because any O2 consumed at the cathode is regenerated at the anode. Hence, equilibrium technology doesn't consume itself like diffusion does over time.
Considering the relatively high investment in industrial quality DO instrumentation, keeping the cost of ownership down can be a factor in looking for a DO probe.
Because DO probes use excitation and low level high impedance internal circuits, DO probes are always sold with a DO analyzer or transmitter which conditions the DO signal to a conventional industrial output. The DO probe does not connect directly to a PLC analog input.
Dan
All products that I am aware of have two pieces - probe and analyzer/transmitter. You can get what you need for outputs or communication (4-20, Profibus, Fieldbus etc..).
Follow Tom Jenkins' advice with the manufacturers. I have used E+H and Danfoss successfully in large / many installations for aeration basin DO control. All probes will require periodic maintenance, cleaning and verification or zeroing but are reliable.
Does anyone have experience using a TDS (Total Dissolved Sensor) w/ a PLC analog input. I have a customer trying to move from a control box and...
11,536
Hi Guys, Could someone guide me as to which is better or reliable to use when conducting a pressure cals? Thank you in advance.
2,706
this is one of the assignment that i have been given in my training course, i really don't understand the way to do the calculation required for...
11,600
Hello, I need a transmitter to measure the oxygen level in an enviroment that can be as hot as 800C. 4-20mA output. Suggestions?
1,600
Hi all...I currently have an ab ML 1100 with a program that needs to incorporate a PID loop based on an O2 sensor. I have no experience with O2...
23
5,914