I don't know for a fact but by implication it is the suppy to the light curtain. Maybe the symbol is trying to represent a vertically standing light curtain.. but then again there is no ground shown...
I see this symbol a lot on European schematics. I believe it indicates the common/ground connection for a DC supply.
In your example schematic, the safety relay appears to be AC powered. Since the light curtain outputs are presumably 24VDC, there needs to be a return path which is why the DC common from the curtain is shown tied to the safety relay.
I’ll second the above on the symbol. We use a lot of sew motors and on their encoders this is the symbol they use for 0v/earth.
I believe it is a coded / pulsed DC signal, so the safety input recognize that the sensor is active and not bypassed... I've seen this as a problem from some safety laser scanners. There was a recent thread about this as well.
This is what I was also thinking since it is wired to S21. You would not want to ground the S21 since it typically is a 24V or or a pulsed output from the safety relay.
Kolyur and Dock have it right - this is a very common symbol for "ground", i.e. your zero volt connection.
The whole thing perplexed me every time I look at it. I am confident in the symbol meaning, whether or not that is the designers intentions, that’s another story.
It's not necessarily "ground", although it might be. That symbol is denoting the NEGATIVE rail of a DC power supply. The positive rail would be a normal "T" shaped symbol, but in this case they have two positive rails, so they are numbered instead.
So does this mean wiring the S21 and S22 to the DC Common does not cause a problem with the relay? If that is the case, what about the short circuit sensing?
Nope - see this diagram, also from the manual.
Normally your safety device has one contact between S11/S52 and S12, and one between S21 and S22. But in the case of a light curtain, you need to disable the "test pulse" checking and short circuit checking, because the light curtain does it's own diagnostics on that front. To do that, you connect S21 and S22 to zero volts, and the relay then knows that it's looking for two 24VDC inputs on S52 and S12.
Bit of an odd way to do it, but the diagram from the safety relay manual matches the diagram from your light curtain.
I don't use those safety relays any more; they're long superseded. I use the 440R-S13R2, which is a bit less creative with it's wiring methods.
Good morning all, I am working on an electrical schematic for a conveyor panel. I found this symbol from this website, which I imported into...
17
6,687
Hi! Has anyone got symbols for the AB conversion modules 1492-CM1771-....? These are modules used to convert 1771 series to 1756. Thank you
2,106
I have inherited an existing project, about 8 years old, at a chemical plant (think, Class 1, Div 2 environment). I cannot identify this device...
4,006
Sorry for the missing JPG If the Electrical symbols shown are used for Pushbuttons which symbol will you use for a “Two Hand Tie Down Optical...
9,030
Hi everyone, I'm in search of software for electrical drawings, preferably free but also interested in paid options. Any recommendations or...
33
1,592