Encoder Issue (Siemens Step 7 FM350-1)
CallumMacEwen
Jul 2015
Scotland
42
Hi All,
First time I have ever worked with encoders and I am having a slight issue. The encoder is set up counts up and down and works well for the most part.
Every now and then though when the motor stops the encoder will still increase.
I have verified that the motor has stopped and I have checked the voltage coming from the encoder and it is not pulsing.
Does anyone have any idea why this might be happening?
What encoder connections have you got and how have you configured the FM350? If you have pulse and direction signals, then if the motor stops on an encoder edge you will get counts if there is any vibration.
What kind of encoder ?
If it is a full quadrature encoder with A/B signals, then it should be impossible for the count value to creep even if the encoder is on the edge of changing status.
I think also a half quadrature encoder is immune against this.
On my machine we have MicroMaster 6SE6400-1PB00-0AA0 running a motor with a Siemens 6FX2001-5QP24 encoder. Everything was working fine and then...
305
I am trying to set up an Allen Bradley 842-E-CM-S encoder in a Control Logix L81E I have it configured and the ethernet sees the encoder with no...
1,401
Hi, Everyone I am interfacing rotary encoder(incremental encoder) with PLC. This encoder using for speed measurement (RPM). The encoder is giving...
4,567
Hi Guys I am currently commissioning a AC890 Drive which has been setup in servo mode using an Heidenhain 1331 encoder. I did not design the...
1,521
a little back story on my machine. It is a cut to length machine running via a Zeta 6104 controller. the encoder is operated by the 1/2 round...
27
4,831