Hello,
We have the following DI card that can accept 1,2 and 3 wire DI's
( 6DL1131-6BH00-0PH1). We plan on installing this card for use with think top head valve limit switch. From the valve manual it says that connections should be made to pins:
1 and 2 for power supply and
then either pin 4 or 5 for valve indication.
Say for example we are going for pin 5, my question is can this be wired to the card in the following way
a wire from uv0 ( +) on the card to pin 1 on the valve
a wire from DI.0 on the card to pin 5 on the valve
a wire from 0V ( -) to pin 2 on the valve
Am i correct that this is a 3 wire installation and can be connected up as i have described or is there something i am missing.
Yes, you have it correct.
What I found quite confusing is there description of the input module as Sink input (PNP, active high).
The wiring diagram clarifies the intended meaning though
Thanks for the reply. Would UV0 and DI.0 not work? Is it not the same as UV5 and DI5?
Thanks again
Yes absolutely. I thought you were going for Pin 5 on the input module but you are correct, any of the inputs with their sensor supply will work.
Hello,
Dont know if its the late night and bad eyes but you could use pin 3 on the valve as well. pin 4 and 5 will give you separate limits and pin3 both. Need to see check the manual when the output in pin3 actually switches
Just to add to my original question. I believe the way I have described above will work but I have also been thinking about the following
Would we need to take a Separate 24V and oV from our panel to the think top head and return to the card via pin 4 on the think top? As would we not be powering the thinktops io board, can the card do this?
Hello, We have the following siemens DI Card 6DL1131-6BL00-OPH1 ( 32 channel) my question is in relation to the wiring of this card with the V50...
887
Hi, I have a question regarding the DI module 6DL1131-6BL00-0pH1, i am confusing myself with the family of IO, this is a 32 channel module. Can...
990
Hello, We have the following DI card that can accept 1,2 and 3 wire DI's ( 6DL1131-6BH00-0PH1). We plan on installing this card for use with a...
1,487
Hi all, is it safe to remove AI / AO / DI / DO card from ET200x (S) while its powered, I would like to see which OB events occur in such...
2,293
Hi I have a task to change a controlsystem on a plant. The existing PLC is a Siemens IM 151-8 with a profibus mastercard 6ES7-138-4HA00. My plan...
632