External monitoring of plc sequence
Kreken
Aug 2013
Norway
Hello guys, I need to monitor a critical shutdown sequencer in order to guard against for example programming errors. If the sequencer does not "do its job" I have the option of enabling the backup relay logic shutdown system. I need some way to monitor along the lines of:
after x seconds a has not happened -> enable backup system
after y seconds b has not happened -> enable backup system.. and so on
Is this a known problem, how does one go about solving it? hardwired timing relays?
any help appreciated, thanks :)
Use a safety PLC and rest much easier. If you do need a secondary system use redundancy modules or another plc of a different brand for cross checking and takeover.
This is how safety used to be done in many cases with 2 plcs of different brands in conjunction with hard wired safrty's also.
I would do a risk assessment first as a single safety plc will likely fit the bill in most cases.
I have a few questions about Studio5000. 1. Why is my RA folder so big? its well over 100 GB. 2. How do you delete versions or extra files...
292
I am trying to enable an external alarm via computer speakers for Factory Talk Network Distributed Edition. I am using Alarm and Events setup. I...
187
Good evening all! I hope you folks are doing alright today, as I've got a situation that I believe I've come up with a solution to but I wanted to...
469
As the title says, I'm trying to figure out a way to import and export recipe files from an external CF card to a USB drive and vice versa. I've...
508
Hi All, I'm using Studio 5000 ver 30 to modify existing logic that has PID, and I want to be able to use an external/remote source as a setpoint...
646