Hi!
I have a motor without brake on an Mitsubishi FRA520 frequency inverter. When I stop this motor it still turns 1 1/2 revolution. This results in a 3 centimeter overshoot from the stop position. We tried DC injection braking without result. (Maybe we made some parameters errors?) Can anybody give me some hints/tips to solve this problem?
(Other solutions are using a mechanical brake or adjusting the sensor wich indicates the stop position. Unfortunatley both options take up a lot of time to achieve. Ofcourse this time is the problem, we don't have it. The parts must be shipped to Japan.)
Thanks!
Rod,
We have a sensor connected to a digital input on an S7 300 PLC. The frequency inverter is controlled by digital outputs of the plc. So we have a start signal to the STF connection on the inverter. I know there is a delay caused by the plc cycle time. But the "overshoot" is to large to be caused by this delay.
Try a slow down limit switch to change the speed to a lower HZ before final stopping point. How fast is the motor moving when it is shut down?
The problem is that changing the sensor (or building a new sensor) is not an option. We will have to do with the sensor we have. At this point the motor is turning 60Hz. But with software we can change it to slower speeds (Time running then to slow speed)
I don't know if this will help or even if its valid on an A500 but here's the procedure to help the stopping accuracy on an E500 drive:
1). Read and record value of PR. 77
2). Change PR.77 to 801
3). Change PR. 248 to 1
4). Change PR. 77 back to original value.
Mr Talbot,
Are you sure that these are parameters for a E500?
Valid numbers for parameter 77 are 0, 1 or 2 only.
Parameter 248 doesn't exist.
Werner, your best bet is to set the drive to ramp to stop (not coast), then set the decel time to the short amount of time you need. This will almost certainly cause the drive to fault on High DC Bus Voltage.
To take care of that fault, buy a small snubber brake package for this drive from Mitsi. Usually, it attaches to the DC bus terminals and will waste the braking energy as heat in its resistors. You will need to mount this package somewhere where the occasional heat can be dissapated without damage.
With a properly sized snubber brake, you will be able to develop as much braking torque in the motor as you have motoring torque.
This is the maximum amount of electronic braking available without buying a bigger drive, motor, or both.
Hi All, I've been playing with 2 stratix switches in my test bench and seeing how different configurations affect the behaviour when 2 managed...
251
Dear all, Im using Allen Bradley Compact Logix L36ERM as a PLC. and facing a problem where I need to create a FIFO buffer that fills an...
1,671
Dear Members; We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when...
1,873
Hi all, I have several machines utilising a PF755 on CIP motion. Occasionally the operator reports the jog speed ramps up rapidly, then the drive...
1,374
Hello guys, this is my first post on this forum and i hope u can help me. Im doing a project where we need to read data in the Wincc Professional...
1,053