fault code=001h Reason???
sultanahmed
Jul 2013
home
63
Dear All,
I am working on machine in which Allen bradley SLC 5/03 CPU (1747-L531E) is installed,i am having error again and again don't know why?? Each time i got error fault code=001h
when i try to go online no program available after that i download program then PLC goes normal,after a week got same error.
i checked battery which is ok
after each download PLC works fine.
What exact error reason is this??CPU?? Battery??power supply??any module??? :confused::
please help
Error is attached
You don't say how long this has been occurring...
If the battery is good it should not matter if the PS had a blip as far as keeping the program intact.
Check all your PS connections though, cycle power on purpose and see what happens.
Rarely seen in my experience but perhaps you have a flaky Processor or PS
.... or a module in the chassis pulling the PS down momentarily because of something connected or a programmed activity the module is doing. It may not be as random as you think, See what is taking place with the PLC, connected I/O etc. when this happens.
Can you connect anything to the plc to monitor power to see if it drops momentarily?
Well that is interesting and I would not dispute it but I did say
"in my experience but perhaps you have a flaky Processor or PS"
Always good to start with a PS but I would not have guessed that alone considering the battery is good. Never seen a processor loose the program because the PS went dead.
But thanks for the tip!
ANY OUTPUT
We had a similar issue that was caused by an alarm/buzzer directly wired to an output that was internally shorted pulling down the power supply causing the processor to fault. It was difficult to troubleshoot because the alarm/buzzer was intermittent, once every week or so. After disconnecting the buzzer the faults went away.
You might want to inventory all hardware devices that ARE NOT isolated, any questionable devices directly connected to outputs should be isolated with a relay as a standard.
Any one give solution for this fault. We are using AB Gaurd logix controller(5573s), resent days we are facing major fault in controller...
52
I migrated to a WSP2023 application. Now when I open a HMI object (for example a valve or motor) the popup is first correctly show as defined ...
33
We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
114
Good morning everyone I’m currently working on a omron device net and have a nord drive that fell off the network. I have limit knowledge in...
133
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
89