Fault with soft starter
Bill.c1
Mar 2018
Nsw
Motor takes 3 or 4 starts to reach running speed
Also stops when running on fault 17 no load b
Control is through PLC conns link
And to what kind of machine is that motor connected ?
is it a difficult starting machine?
like a big centrifugal fan?
Allen Bradley SMC flex
Connected to 100 kw motor wood chipper in saw mill
Has been running for past 5 years
I have power monitor connected now and will check later
How do you check control module on starter
No Load B means the current flowing through Phase B is less than 20% of the rating of the starter. My first thought is that you have a loose connection somewhere. On a chipper, it might be at the motor connection box due to vibration. Could also be a failing motor winding, but I always like to eliminate the cheap things first.
Don't start by assuming the control board is bad, assume it is doing its job and protecting you from a bigger disaster. Eliminate ALL other possibilities first. Generally if a control board is bad it just ceases to function, not start acting squirrely.
Hi friends recently one month back i commissioned 220kw ss with 420A(200KW) load but today fault occur in soft starter.The fault is open bypass...
3,520
Is there a way to get the fault history from a SIRIUS 3RW4456 Soft Start through the HMI keypad? I've been through the manual but it is pretty...
746
Hi guys, Some of you may remember me mentioning a backup Profibus connection I have in my project. A quick recap: 1. Existing Profibus...
3,243
I'm using a Kinetix 6000 to drive a ballscrew. The axis was jogged into the maximum negative soft limit and the drive faulted. The fault action...
8,347
Hello, iv made up a fairly basic program on twidosoft but random faults keep appearing in it. On simulation and on live mode when running on the...
1,965