Faulted A Processor Today
Mispeld
Feb 2017
VA
644
People were not happy, to put it politely.
Added a PID instruction with the following configuration...what's wrong with this picture. Hint: It is obvious.
Faulted the processor because the EU minimum was larger than the maximum? And it let you send it to the PLC without a warning? If so, that's a pretty severe penalty for a mistake that's easy to make. What PLC?
Yup, swapped the minimum and maximum engineering unit values. Faulted on the first scan of that PID instruction.
Having experience with this particular fault, I had been careful to check the initial set point value. And also have limit checks on every MOV into the .SP register. Then this error slips though, and the dreaded red FAULTED.
The processor is an AB PLC-5/80, and I was using the latest version of RS-Logix 5. But, really, I don't cast blame in that direction. Probably should have had someone else review the code before activating it.
I just programmed a PID control system for a VFD to control header pressure for our weak liquor pump to our evaporators. I tested out all the...
1,898
I have an application where I am doing a MSG read from "PLC_A" reading "DINT_1" in "PLC_B". What happens if PLC_B faults? Will the MSG read still...
2,629
I have a PLC 5 that has a faulted processor, can some one tell me how to see why it is faulted and how to reset the fault? I have not messed with...
2,385
U
I have a SLC 5/01 processor faulted that was programmed with AI series long time ago. How can I clear this fault with RSLogix 500? If it can not...
2,236
Hi I have hms-en2mb-r module . When i configure and go online the module is faulted with error code 16#0009 and addition code 16#0001. Is there...
730