Finding my SLC 5/03...
showshocka
Mar 2011
USA
510
hello. i have an SLC 5/03 that i am having no luck with gaining an Ethernet connection, i don't know the network address to the PLC. the pwr supply door is not marked like the rest of the PLC's in the plant. my laptop is configured correctly, i can log on to other plant PLC's easily.(because i know the addresses and they are listed in RSlinx)i am also pretty sure that it's not added to the list of devices in the RSlinx network addresses as well. is there a way where i can find out the PLC's network address using some type of windows software tool or some other setting.....
The little plug on a 5/03 is not ethernet. It is DH485, so there is no windows tool to find its node number. If you have a DH485 device connected between the PC and PLC (1747-UIC, or 1747-PIC) then have a driver configured in RSLinx for DH485, it should appear when you browse that driver.
It is possbile to damage your laptop ethernet NIC by connecting to a DH485 port on a SLC, so be careful.
If you have a DH485 device connected between the PC and PLC (1747-UIC, or 1747-PIC) then have a driver configured in RSLinx for DH485, it should appear when you browse that driver.quote]
yes that's what i did. i just wanted to also view it with ethernet connect
To repeat the SLC503 does not have an ethernet port, there is 24volts on 2 of the pins, so you will more than likely damage your computer (these are used to power a 1747-AIC comms module).
As OkiePC says you will need to use either the 1747-PIC if you have a realserialport and Windows XP SP2 or earlier.
If you do not have a real serial port then you will need to use the 1747-UIC and CP13 cable ( it does not have the wires that connect to the 24volt connections of the plug on the SLC503 port)
Do not use a standard ethernet cable as the 24volts from the SLC503 can fry the 1747-UIC.
Alan
Can this be read on RSLogix 500 when online? I don't see it under controller properties. The sticker on the CPU side says "1747-L552 ser C FRN 5"...
3,417
Looking at 6 Integer values...say N7:0 - N7:5. Need a clever way to find the Minimum and Maximum values from this group. Better yet would like to...
6,347
Hi all, I'm in the process of upgrading a PanelView1200 HMI program to be developed in FactroyTalk View Studio. The filetype for PanelView 1200...
322
Hey all, pretty new to PLC and got a question regarding finding the MSB or the last non-zero bit in a SINT array in studio5000... I am reading...
858
Having an issue connecting to my Micro820 PLC. I don't have an IP Explorer and I know its MAC Address is 5C:88:16:D8:E6:65. I'm connected to the...
965