fine tune PID loop
hani2018
Apr 2018
New York
20
I am troubleshooting a PID loop developed and tuned by others. It is a heat exchange process, utilizing steam and control valve to heat up process water from 0 to 80 degree in 1.5 minutes. PID equation is independent and current Kp value is 25, Ki value is 10 andn Kd is 0. See attachment for trend of PV and CV. CV open from 0 to 100% and PV obviously go into oscillation status.
What procedure shall I follow to identify right Kp and Ki value and allow temperature to reach SP fast(in 1.5 minutes) and without overshoot?
Thanks very much for your help!
It looks like you are ramping the CV before you start the PID. Was that intentional?
There is no time scale in the image you uploaded. There is no frame of reference here.
What is the PID update rate set at?
Is the PID running in its own task?
It would be more helpful to see the open-loop step response. This is the CV and PV trends with x and y axis values shown for a manual step change in the CV up until the PV settles, and then down until the PV settles. Also needed are the PV scaling values in the PID block.
Thanks for help first:
To answer ndzied1 questions:
(1) No CV start to ramp after PID start. It is trend type selection result.
(2) See new trend diagram attached for time scale
(3) PID current loop update time is 0.5 sec
(4) PID is running in its own periodic task, period setting is 250ms
To answer Mispeld questions:
(1) Can't get open-loop step response today because of production
(2) In PID block, PV scaling value range ( see attached diagram 2)
Just wondering
I'm Not an expert at this but I'm wondering...
1) why do you stop the PID after the set point is reached? wouldn't you want to leave it on so that it can reject disturbances and maintain the set point?
2) would Feedforward control be a good choice for this application? if the demanded temperature and flow rate can be known and the input steam temperature can be known then there could be a calculated steam flowrate based on the properties of the heat exchanger system and have the PID just keep out unknown disturbances?
If the PID instruction unconditional in the periodic task, then loop update time should be equal to the task period (0.25 sec). Changing that will affect the integral action, and is helpful when computing model-based tuning gains.
With the gains you have specified, and the time scale on the trend chart, I am not understanding why the CV is staying constant for the first 10 seconds after the initial proportional action upon starting the loop, which I interpret as switching from manual to auto with an error of about 75 engineering units. That initial action seems about right for the error and proportional gain.
It seems as though there is some extra logic manipulating the mode of the loop or the CV immediately after "PID start." I would expect to see the CV continuing to increase at a steady rate due to integral action during the 5 seconds of deadtime, and then increase at a slower rate as the PV starts to come up. Instead, it looks like the loop is suspended until the PV is around half way to set point. Is there any logic that manipulates the .SWM bit with a timer?
While deadband shouldn't behave like this, is there a non-zero deadband setting?
It may not be the Contrologix that does this, I can’t remember. It’s one of the AB PLCs.
Without setting a max CO and min CO, the integral calculation will “run-away” or windup.
After passing setpoint, the integral must then wind down and once it’s below, it will wind back up.
I don’t suppose you are dipping anything in the tank? If not, then why would integral be needed?
The PLC-5 (PD version) and CLX PID instructions have anti-windup integral action defined as suspending increase in the integral term when the loop CV reaches max CO, and similarly for decreasing integral at min CV.
In looking at the trend, it might be possible to explain the behavior of the SP, PV, and CV if "PID start" refers to a step change in set point with the loop already in auto, as opposed to a transition from manual to auto (i.e., clearing the .SWM bit).
In the former situation, with the loop output (CV) at what looks like zero percent, it is likely the integral term has accumulated some negative control action, though clamped by anti-windup, which must be overcome before contributing to a positive CV movement. Even so, I would not expect a constant CV, at least if CV in the trend is the unmanipulated .CV computed by the PID instruction.
Thanks for everyone's instruction.
I review the logic, there is timer and pid.maxo limitation logic in current code. When PID is enable/start, a 10 second timer will run and PID.maxo is limited to 30% in 10 second, after timer is done, maxo is changed to 100%
Please see attached excel file for PV an CV historian data.
Deadband value PID.db is set to 0 in current configuration. PID start/stop is linked with water supply pump status. Supply pump is run by process for 1.5 minutes and then stop for a while and run again and repeat this process for couple of times.
Shall I disable the timer and maxo limitation logic?
I will increase task pid task periodic time to 500ms to match loop update time
After above fix, what procedure shall I follow to identify right Kp and Ki value and allow temperature to reach SP fast(in 1.5 minutes) and without overshoot?
I don't have a way to chart that data table, but from your previous chart, I would speed up the loop update to 100ms (no downside). Yes, try disabling the maxo timer logic. Also, one or both of your gains are too high. Try lowering the P gain first.
hello dear forum, About DELTA DIAView SCADA I defined a variable in Timescript VBscript I want access this variable from within a window For...
588
I have a mechanical press. We are having problems and we believe it may have something to do with the movement and speed of the press. The press...
1,461
Hello PLCS.Net! I have the EDS Hardware Installation Tool installed on my PC. When I try to install a file, It says it's successful, the...
2,038
I know we have discussed these in the past but I found this and its a warning to some, this is in a spreadsheet but I think they could find the...
29
9,378
Good evening all, We have a couple of volumetric fillers at the brewery where I work. We monitor & weigh our bottles to ensure we are legally...
1,667