Hi Gang,
Haven't been by in many moons. Too busy.🤾
I have run across an issue I cannot resolve. I have an application that was installed in the spring, so recent software versions. I have a Rockwell FactoryTalk Historian, and a FactoryTalk SE (distributed) server. I am collecting data from a 3rd party and displaying it and historizing it too.
I have a performance equation running in the Historian that selects the highest value from a set of tags, and the averages the highest value. I want to display the result in SE, but cannot seem to do it. I have tried {FTHistorian::Mytag} which SE says is valid, but nothing displays.
In the short term, I have embedded a small 2 x 3 Trend in the graphic, which shows the tag historical and current value. But it's not ideal.
Thanks,
Ken M.
Called Rockwell Tech Support this morning. It's possible, but you have to go around your elbow to get where you need to be.
Since the FTHistorian is connected directly to the PLC, not the HMI. The Historian can write a value to a tag in the PLC. Then in the HMI, I read and display the PLC tag. I tested it today, and it works.
-Ken
I noticed that the new FTHistorian 9 only uses the PI 2018 still, and is not updated to 2023 yet. I figured by now any new releases would have...
178
Hi, I managed to read all the tags and value from AB control logix but I had problem to read HMI tag and value from FTView SE, can anyone share...
3,206
Hello All, I need the ability to remotely reboot a Red Lion CR3000 HMI. Due to some graphics issues when the database is updated the HMI must be...
230
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
355
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
186