FTview MeStation :Can use Goto display button as momentary push button ?

minaykha

Member
Join Date
Apr 2009
Location
singapore
Posts
96
Hi Everybody,

is there anyway to use Goto Display button as a Momentary push button ?

When Goto display button is pressed, i need to change the HMI screen and at the same time i want to write a value to PLC program.

I am using Factory Talk Me station and Rslogix 5000 software.

Any Suggestion ?
 
Hi,

We use the 'Global connections' option and use the PLC if we need extra functions regarding screen control (see attached image).
You can then use the action of a button to control a tag in the PLC and then use that tag to write to your screen control. Note - you need to reset the screen WRITE tag value to 0 if you want to use the regular FT navigation...


Regards,

Rob

2014-01-10_093851.png
 
Hi,

I just normally check for it not equal to zero, then (after a delay) move zero back! (see screen shot attached)

Hope this helps!

Rob

FTV Scn Rset.jpg
 

Similar Topics

Hello, I am fairly experienced programming and modifying existing FTView ME programs. I have also used FTView SE to make modifications to a...
Replies
5
Views
113
Hi folks. I have a system that I'm working on that needs 2 alarms banners with different event subscription: - One banner for a specific area...
Replies
6
Views
203
Hello guys please I want experience with this I am currently working on a scada project using FTView SE and I have an Ethernet IP local area...
Replies
0
Views
51
I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
Replies
4
Views
202
I want to set user security level based on the value of a tag in my PLC called "ActiveUser". That tag will contain the A-P code which we use for...
Replies
6
Views
248
Back
Top Bottom