Hi Friends,
Please, who can tell me the Function Block used for scaling 4-20mA to say 0-200PSI in Mitsubishi GX Works3?
I know nothing of GX Works3, but in general built in functions aren't always needed, write your own scaling function:
Code:
// Scaling uses this formula:
// Ov = [(Osh – Osl) * (Iv - Isl) / (Ish – Isl)] + Osl
// Ov = scaled output value
// Iv = analog #Input value
// Osh = high limit OF the scale FOR the scaled #Output value
// Osl = low limit OF the scale FOR the scaled #Output value
// Ish = high limit OF the scale FOR the analog #Input value
// Isl = low limit OF the scale FOR the analog #Input value
Code:
Ok Bro. Thanks for the response.
Assuming a 4-20mA to 0-200PSI Scaling, From above: Do you mean
Osh = high limit OF the scale FOR the scaled #Output value=200psi ?
// Osl = low limit OF the scale FOR the scaled #Output value=0psi ?
// Ish = high limit OF the scale FOR the analog #Input value=20mA ?
// Isl = low limit OF the scale FOR the analog #Input value= 4mA ?
// Iv = analog #Input value (SHOULD THIS BE THE TAG)?
If the Input Value is in mA, then yes.
On the PLCs I use the Input Value is the output of the Analog block and in the range of 0 to 27648. So for me Osh and Osl would be 200.0 and 0.0, Ish and Isl would be 27648.0 and 0.0. You will need to be working Floating Point numbers.
You are right. Resolution 0-27648 for siemens, 0-16383 for AB SLC.
I need to figure out Mitsubishi's Resolution,
I Trust some one here will have an idea
The 0 to 27648 I gave would be for a 0-20mA signal, 4-20mA would be 5529 to 27648. 5529, is 27648 divided by 20 multiplied by 4.
I am new to this forum and would need your help. I am looking for the Modbus FBs for the S5 95U for communication with the CP521. These FBs...
55
Hi, I have attached herewith one image which our programmer has been used in S7 1500 PLC. Now we need to use the same instructions in S7 1200 PLC...
154
Please see attached file. I need this program in Function Block form but I am totally lost on this. Any help would be appreciated. Thanks!
345
Hi! I am using a TM200CE40T PLC from Schneider to write data over Modbus. I have used Memory words (%MW) before using the Write variable...
561
Hi folks. New to the forum, but been working with PLCs for several years now. Would like some advice on whether you would keep this logic, or...
1,103